Old 06-26-2007, 09:14 PM   #1
Help with voltage troubleshooting
One of the electrical outlets in my bedroom suddenly failed. I've lived in the hosue for 7+ years and I replaced the receptable at the outlet about a year ago. Never had any problem until yesterday. Took a voltage measurement at the line and got 27V instead of the 120V that all the other outlets have on the same breaker. One potential issue I observed was the neutral wire has a spliced extension. The splice was covered by tape so I removed the tape and took a voltage there too but still got the same 27V. Would appreciate any pointers on troubleshooting this. Thanks.
epicurux is offline   Reply With Quote
Old 06-27-2007, 05:10 PM   #2
Master Electrician
JohnJ0906's Avatar
27 volts where?
Are you measuring black - to - white? Black - to - ground?
Measure both, and let us know what your measurements are.
Check white to ground too, just in case.
John from Baltimore
One Day at a Time
"Experience is what you get when you were expecting something else"
"The bitterness of low quality lingers long after the sweetness of low cost is forgotten"
JohnJ0906 is offline   Reply With Quote
Old 06-27-2007, 07:50 PM   #3
Thanks for the reply.
I got 27V from hot to neutral and hot to ground.
I haven't tried neutral to ground, yet.
A friend suggested that I should bring a good hot line from another outlet via an extension cord to verify the neutral is good.
Will give 'em a try tonight.
Old 07-01-2007, 03:17 PM   #4
J. V.'s Avatar
So you had this recept working for 7 years and then AFTER you installed the second one it failed too?
Double check the connections on the new recep and any other wires in this box. Make sure that the little jumper that connects the two hot and two neutral on the recep has not been removed. This jumper is to seperate the the two hot screws and the two neutral screws. Both jumpers need to be intact unless you are switching this recept.
Measure voltage from black (hot) to white (neutral). If 120 is not present, then check the black to the green (ground). If you get 120 your neutral is open somewhere. If you still have no voltage find the recep ahead of the bad one. Look for an open connection in this box.
You may have to open several receptacle boxes until you find the culprit.
J. V. is online now   Reply With Quote
Old 07-02-2007, 02:40 AM   #5
Thanks for the reply. The outlet had worked flawlessly for a year after I replaced the receptacle.
As I have stated in my original post. I get 27V (not 0 or 120) from the line and (hot to neutral) that just baffles me. And ALL other outlets on the same circuit are working.
I took voltage from neutral to ground and got nothing. Very puzzling ...
Old 07-02-2007, 08:51 AM   #6
Licensed Pro
The 27 V you are reading is a "phantom" voltage and should go away if you place a load between the meter and the hot. Check any splices you have in that box and all connections at the closest working receptacle on that same circuit. If you have backstab connections, the problem is most likely there. Under normal circumstances, you should read 0V between neutral and ground.
Low voltage Light Rze Electrical 4 04-21-2007 12:38 PM
Troubleshooting bedroom outlet wiring? Operator4819 Electrical 15 04-01-2007 09:10 PM
Low voltage to vacuum l.schrankel@comcast.net Electrical 2 03-04-2007 10:38 AM
Which low voltage wire scozzer Electrical 2 02-18-2007 11:56 PM
Voltage At House Outlets bobo Electrical 2 02-04-2006 12:25 PM