Help With Tapped Sub Panel. - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 07-05-2013, 02:53 PM   #16
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Originally Posted by wirenut1110 View Post
The difference in service rated and non-service rated is the center off position.
These switches don't have any OCP but have the center off position and are listed for use as service equipment.
I just got in a disagreement on another forum because I would think it needs some sort of OCP. Just isn't always what I think...lol
what about 230.208?????
Old 07-05-2013, 02:58 PM   #17
Electrical Contractor
wirenut1110's Avatar
Rewards Points: 510
Send a message via AIM to wirenut1110
I totally agree and it seems like it's "equipment on the line side of the service" in which a generator ain't one of them that's allowed.
I've talked to some local inspectors about it also and they said they would allow since it's close to the meter and "service disconnects".
I was like "SOB, if I 'd had known that I'd be using those instead of what I've been using".
wirenut1110 is offline   Reply With Quote
Old 07-05-2013, 03:00 PM   #18
E2 Electrician
You can't do it, it's a clear violation.
Old 07-05-2013, 03:01 PM   #19
E2 Electrician
Every service rated ATS i've ever installed comes with a circuit breaker.... its pretty obvious why.
Old 07-05-2013, 03:08 PM   #20
E2 Electrician
And I guarantee they are NOT the AHJ and should not be allowing this.
Old 07-05-2013, 03:08 PM   #21
Rewards Points: 510
Here's a PDF on the Ronk switches. Very similar to his, his looks like a GE.
http://www.ronkelectrical.com/pdfste...RRITE%20GL.pdf
Notice the switches rated SUSE because of the center off position.
Old 07-05-2013, 03:15 PM   #22
E2 Electrician
I know, I was just questioning the fact if it was service rated, it would make sense that the "OFF" position would indicate that, and i did forget the OCP can be after, but it needs to be 'immediately adjacent too' so whatever that means...
Old 07-06-2013, 06:57 AM   #23
ericmunyon12345's Avatar
This is your best bet, with what your trying to do.
Also, you couldn't "tap" that with #6's anyway.
Just because this isn't inspected doesn't mean you shouldn't do it right.
Just to understand, why couldn't I use #6 if it is just feeding a 20 amp breaker in a box right next to it? I know normally you can't drop wire size (based on opd rating), but I heard rules are different for "taps." Again, not challenging you, just want to understand.
ericmunyon12345 is offline   Reply With Quote
Old 07-06-2013, 07:57 AM   #24
Rewards Points: 510
I'll try to answer this, hopefully someone that's more in tune with all the wording and definitions of the code can verify, clarify, or deny this.
Maybe I'll learn something with this discussion.
The conductors feeding this disconnect are tapped conductors. You can't tap a tap.
The conductors after this breaker is a branch circuit, and the conductors need to be sized according to the OCPD with exceptions like motors, hvac equipment, etc.
To me, this would be no different than having a junction box with, let's say, #10 conductors in it and splicing a #14 wire to it and call it a "tap".
The Following User Says Thank You to wirenut1110 For This Useful Post:
ericmunyon12345 (07-06-2013)
Old 07-06-2013, 08:32 AM   #25
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
I've said this before, but I'll say it again, the tap rules confuse the hell out of me, but I found this to be useful and it appears that he could tap 6's off the load side of the 100A.
http://ecmweb.com/code-basics/unders...es-feeder-taps
Old 07-06-2013, 08:39 AM   #26
Rewards Points: 510
I read the same thing before posting.
In some of the wording, it appears to be ok then, after reading into some other articles and definitions it appears to be not ok.
Old 07-07-2013, 04:03 PM   #27
Ok, K Buzz has me asking if my plan to tap off the load end of that would work. They trimmed those conductors, but they're way bigger than 6, do I just need big split bolts and doesn't matter that the tap line is thinner?
With regards to "can't tap a tap," I agree, but would it still have protection if tapped to the load side of that 100 amp? And this confuses me, if anything after the transfer switch is a tap...which can't be tapped, why are there a couple mercury lights tapped from the load sides of those disconnects? I just want another one (except I'll do a flood and thought if I did a 2 space panel with a 20 amp breaker, I could do a plug and the flood. If they can tap for mercury lights from the load side of the 100 amp disconnect, I still don't understand why I can't add at least the light (75 w.) finally, regarding the discoloration on the lines into that far left disconnect, is it possible the installer just didn't use anti-ox? (All those panels were professionally installed.)
Old 07-08-2013, 08:34 PM   #28
More help, please. Some conflicting (apparently) answers.
Old 07-09-2013, 02:27 AM   #29
Electrician
Rewards Points: 150
Can you post pictures of the 100A disconnect on the right? Especially of the whole box with the cover off? Being physically bigger it has more room for legal splices(taps). And it may not be a scary train wreck like the one on the left.
You could use outdoor listed Liquidtight Flexible Nonmetallic Conduit (LFNC-B = Carflex) and easily route it over the top of the main. You could mount a four space panel to the right of the main and be in business.
Split bolts have wire size ranges embossed on them. If the large conductor and the small conductor fall within those ranges, you are good to go. They are also embossed AL, CU or AL/Cu. Use only split bolts for the type of wire you have.
...why are there a couple mercury lights tapped from the load sides of those disconnects? *... (All those panels were professionally installed.)
There are good and bad electricians, just like any profession. Cover yourself. Always get permits and inspections.
Anti-ox is primarily an aluminum wire issue. Those wires look like copper. For normal, noncorrosive location, residential wiring, anti-ox is never used on copper.
Glennsparky is offline   Reply With Quote
The Following User Says Thank You to Glennsparky For This Useful Post:
ericmunyon12345 (07-09-2013)
Old 07-09-2013, 04:12 AM   #30
Electrician
Rewards Points: 150
The conductors after this breaker is a branch circuit, ...
It's a branch circuit if there are no other OCPDs (fuses or breakers) on that circuit. If it goes to a breaker panel, it's a feeder. Article 100, definitions.
...and the conductors need to be sized according to the OCPD with exceptions like motors, hvac equipment, etc.
Or taps.
You could do that. If, for instance, the #14 went directly to backfeed a 15 amp breaker. And the breaker was fastened with a hold down kit.
Sub panel to sub panel feeding tvfd27 Electrical 1 08-21-2012 03:01 PM
Section 310.15(B)(6) vs. 210.4. Don't assume, call your friendly AHJs! Daneel Electrical 3 04-11-2012 07:24 AM
Replacement Meter Panel leonard_voet Electrical 19 04-09-2008 10:27 AM
Installing new (service?) breaker panel and generator panel Nhrafan Electrical 6 04-01-2008 03:03 PM
turn main panel into a sub panel? tikicarver Electrical 2 01-24-2008 07:37 AM