ericmunyon12345 07-04-2013 08:19 PM
4 Attachment(s)
I want to pull (split bolts?) from the far left panel. I want to add a two space outdoor panel. I only need one 20 amp breaker for a recep and a 75 watt flood light. Tips on doing this would be great. I think I should tap the line side of that 100 amp box (b/c the load wires are so large for voltage drop...someone actually snipped several of the strands to fit it in the breaker terminal). I plan to use #6 cu thhn/thwn. The line side of that box is still load side of service drop (fed by large box with lever switch / lockout).
In the new two space, the neutral bus stays isolated, right? So, should I just attach the egc from the new plug and light to the box? The new box will be bonded to the 100 amp box via the nipple.
Jim Port 07-04-2013 09:11 PM
Those terminals are for one conductor only. You cannot tap there.
ericmunyon12345 07-04-2013 09:28 PM
Right, but COULD I join to wires with split bolts? (This will not be inspected.). From the sub panel, I would run individual
Conductors in liquid tight transitioning to PVC.
Glennsparky 07-05-2013 03:15 AM
You already have burnt insulation and damaged conductors above those line side lugs. And unsafe hack work on the load side. So, let's concentrate on doing this right. For property resale value, for insurability and, dare I say it, for safety.
If the wire from meter to main was rated for 420+ amps and the wire to the 100A breaker was rated for 120+ amps(it isn't), then we could bother to do a fill calculation. Otherwise split bolts and the tap rules are used on the load side of breakers.
In either case you need a new panel with at least four breaker spaces. Two spaces for a back fed breaker with a hold down clamp and two for the load.
The only way to use that new two space panel is to replace the 100A breaker with a quad. Unfortunately, the largest quad is 50A. Since that circuit is already burning up, 50A is definitely not going to make it.
Glennsparky 07-05-2013 04:47 AM
I think your best bet is to replace that disconnect with a panel. There are a couple of ways to do it. You'll need to do some pricing and research.
You're also going to need to change those line wires from the main disconnect.
You have two choices for panels. An outdoor 100A main breaker panel with feed through lugs.
Or a Main Lug Panel with at least a 100A stab rating on the busses. Get a regular 100A breaker and a hold down kit. Back feed that breaker and use the main lugs for those aluminum feed wires.
Sorry, this is a much bigger job than you bargained for.
wirenut1110 07-05-2013 05:46 AM
This is your best bet, with what your trying to do.
Also, you couldn't "tap" that with #6's anyway.
Just because this isn't inspected doesn't mean you shouldn't do it right.
ericmunyon12345 07-05-2013 07:05 AM
Agreed! I only stated that because sometimes something perfectly safe and functional still isn't code. I may call someone in if there are problems with existing. Thanks.
wirenut1110 07-05-2013 07:22 AM
I'll agree with that somewhat.
I feel the NEC is starting to change for "customer convenience" and to make things "idiot proof" rather than what's safe/unsafe.
Unfortunately, some of the representatives on the code making committees, have their interest in mind rather than what's safe and practical.
However, people have mandated that, this is what they want by the way they vote. It isn't "change" it's dollars:no:
ericmunyon12345 07-05-2013 10:09 AM
So is there general agreement that I should not tap from here? If so, I'll look at trenching from a load center...sounds like it might be less involved.
wirenut1110 07-05-2013 12:39 PM
Not saying that.
Replace the disconnect with one of these.
Take your 100 amp breaker and install it in this panel with a hold down kit.
Then, the wires that are connected to the load side of your breaker now, will then hook to the lugs on the new panel, THEN you will have space for 2 single pole breakers or tandems or whatever.
The wires from your main will hook to your 100 amp breaker therefore, you'll be backfeeding the new panel.
http://images.lowes.com/product/conv...3643322196.jpg
stickboy1375 07-05-2013 01:14 PM
12 Attachment(s)
I dont see how the transfer switch is legal not being service rated and all.....
ericmunyon12345 07-05-2013 02:27 PM
Help me out. Transfer switch=the lever switch that is the main shutoff? Or the 100 amp switch I wanted to pull from?
wirenut1110 07-05-2013 02:36 PM
It is, it has a center "off" position.
stickboy1375 07-05-2013 02:38 PM
12 Attachment(s)
and? is it service rated? Where is the OCPD before the transfer switch?
wirenut1110 07-05-2013 02:46 PM
The difference in service rated and non-service rated is the center off position.
These switches don't have any OCP but have the center off position and are listed for use as service equipment.
I just got in a disagreement on another forum because I would think it needs some sort of OCP. Just isn't always what I think...lol