Help With Switches - Electrical - DIY Chatroom Home Improvement Forum
Old 01-14-2012, 04:50 PM   #1
Help With Switches
hi so i have 2 lights in a room and they both turn on from the same switch but i want to make them seperate switches here is a quick diagram of what is going on the room is finished so i was hoping i could do something with out cutting any holes the switch that controls the recepticle i want to use to control the light to the far right and keep the other light on the 3 way switch to the left any advice would be awesome thanks
Petrafire is offline   Reply With Quote
Old 01-14-2012, 05:00 PM   #2
MarginallyQualified
Rewards Points: 2,464
This depends on two things:
1) which of those boxes has the feed power
2) how many conductors run between the first light and the second
You'll need access to the attic... if so, doable.
(but a lot more work)
Old 01-14-2012, 05:11 PM   #3
1) the double switch box has the feed power
2) 14/2 romex runs between the lights
no access to the attic this is actually in my basement ceiling is finished the lights are actually in 2 different rooms its such a waste to have the light on in a room that no one is in
Old 01-14-2012, 05:18 PM   #4
joed's Avatar
Rewards Points: 12,852
You need to change the cables. In order for the second fixture to get separate control you need a new cable to either of the light boxes in order to get control.
Old 01-14-2012, 05:42 PM   #5
Just take the bulb out....
Bmelo is offline   Reply With Quote
Old 01-15-2012, 07:20 AM   #6
ok so i will have to cut some drywall then
Old 01-15-2012, 07:39 AM   #7
You need to have 2 separate 14/2. One switch to one light and the other switch to the other light. But if you have boxes at lights you could just run a wire to the first light and make a splice there.
Old 01-15-2012, 01:10 PM   #8
thank you
Old 01-15-2012, 05:04 PM   #9
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
Not code compliant to run an individual switched hot wire. All he needs is a 14/3G from switch box to first light fixture.
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 01-15-2012, 05:05 PM   #10
UAW SKILLED TRADES
Stubbie's Avatar
deleted
Stubbie
Old 01-15-2012, 05:18 PM   #11
Not code compliant to run a 14/2 to a light to switch it on or off??? New to me can u let me know what code article. And yes a 3 wire would do the same thing, would just require a splice at the first light...
Old 01-15-2012, 05:26 PM   #12
joed's Avatar
The current NEC requires neutrals in switch boxes.
404.2(C) Switches Controlling Lighting Loads. Where switches control lighting loads supplied by a grounded general-purpose branch circuit, the grounded circuit conductor for the controlled lighting circuit shall be provided at the switch location.
“Exception: The grounded circuit conductor shall be permitted to be omitted from the switch enclosure where either of the conditions in (1) or (2) apply:
“(1) Conductors for switches controlling lighting loads enter the box through a raceway. The raceway shall have sufficient cross-sectional area to accommodate the extension of the grounded circuit conductor of the lighting circuit to the switch location whether or not the conductors in the raceway are required to be increased in size to comply with 310.15(B)(2)(a).
“(2) Cable assemblies for switches controlling lighting loads enter the box through a framing cavity that is open at the top or bottom on the same floor level, or through a wall, floor, or ceiling that is unfinished on one side.
Old 01-15-2012, 05:48 PM   #13
Ok and he said the feed is in the switch box.. Right? And running a 14/2 to each light there would be a switched hot (black) and the neutral. How would there not be a neutral? Am I missing something here?
Old 01-15-2012, 05:51 PM   #14
Licensed electrician
Rewards Points: 1,608
Bmelo is saying the cable to the second light could be spliced to a new cable run between the switch and light 1.
Old 01-15-2012, 06:18 PM   #15
Rewards Points: 3,256
I think this misunderstanding came from using the word "wire". Like you meant just run a single wire to supply power.
zappa is offline   Reply With Quote
Replacing old switches RyanS2000 Electrical 4 09-11-2011 03:21 PM
Replacing multi-use light switches jimclark Electrical 4 08-30-2011 02:05 PM
Question about wiring and voltage with switches and lights rswurth Electrical 17 06-20-2010 11:12 PM
Replacing switches turning into nightmare. RyanD Electrical 19 05-26-2009 06:19 PM
Need help replacing switches in four-way circuit magnolia Electrical 3 05-09-2008 09:40 PM