Help Sizing Subpanel - Electrical - DIY Chatroom Home Improvement Forum
Old 04-05-2011, 09:49 AM   #1
Rewards Points: 129
Help sizing subpanel
I've got about 95 amps in total breaker size in the subpanel. Nothing more than 20 amps. Can I size this at 40 amps?
wease is offline   Reply With Quote
Old 04-05-2011, 10:18 AM   #2
Rewards Points: 324
breaker size doesn't count.load is based on device/appliance load calc's.depending on what you are running,40 amp should be ok.
oleguy74 is offline   Reply With Quote
Old 04-05-2011, 10:34 AM   #3
Rewards Points: 129
Thanks for the reply.
I have 2 kitchen outlet circuits, a dishwasher/disposal circuit, light circuit, and refrig circuit. Forgot I also have a bath gfi circuit. Add 20 amps to that.
Old 04-05-2011, 12:34 PM   #4
Rewards Points: 324
if not wired yet might just go with 50 amp.
Old 04-05-2011, 12:53 PM   #5
Rewards Points: 129
I believe I would need 6 gauge wire for 50 amp. I could move and reuse an existing 8 gauge wire which would help my cause. Just wondering what the inspector will require for this kind of load.
Old 04-05-2011, 01:28 PM   #6
Rewards Points: 324
if you have a total load of 60 amps,if ballanced between the two phases you will only have 30 amps on each leg so 40 will be good.you need 2 hots,1 neutral and one ground.
sizing new subpanel debiasio Electrical 5 01-31-2011 05:36 AM
Grounding a Subpanel Craigman Electrical 25 12-07-2009 08:25 PM
Problems with Square D Subpanel bltglt507 Electrical 16 12-04-2009 09:44 PM
A few slightly different questions on subpanel wiring. Chris Dopp Electrical 8 06-26-2009 10:45 PM