help running electricity to barn
I recently put in a 10/2 wire underground to a barn about 330 feet away from the main panel. Now I am trying to figure the best way to hook it up. I think I have 2 options:
1) run it 120 from the main box with either a 20 or 30 (??? help??) amp breaker to the barn directly to a gfi recepticle and run a switch for a fan/light setup off that. I think that will protect everything. 2) Can I run it 220 with the 10/2 wire to a small panel in the barn, and use the one wire for neutral then ground the box w/ a ground rod? Then run the individual circuts (plug, fan, light) off individual breakers)?Will this provide me advantages in regards to available power and amount ? I probalbly will not be using 220 at the barn. If I went the 220 route would I use 20 amp breakers from the main panel or 30? Make any sense? |
10/2 wire is a maximum 30 amp breaker. You need 10/3 for 220 volt plus neutral. You can get 220 volts with 10/2 but it will not have a neutral. You cannot use the bare copper wire as a neutral either.
To set a sub panel at the barn you actually need 4 wires. Two hots, One Neutral and one ground. The neutral and ground must be seperated. You will also need one or two ground rods. Consider this a 120 volt branch circuit as in any other circuit in your house. You can mount a small 30 amp disconnect/switch in the barn to enable you to bring wires out for recepts and other small loads. 330 feet is a long ways from your house. I would be concerned about voltage drop at the barn. |
All you can do with the 10/2 already in place is have a single 120V circuit. Protect this with a 15A breaker and be aware that once you pull a load in excess of about 6A, voltage drop will be an issue. In other words, lights and a ceiling fan will be just fine, table saws and other large motors will not be.
That help? |
OK, so should I use a 30 amp breaker off the main panel to help account for some voltage drop or 20 amp?
As a general rule, a voltage drop of no more than 5% is acceptable for most equipment/situations. |
I recommend the 15A breaker because once the draw is much more than 6-7A, voltage drop will be an issue, so best to protect whatever he is trying to run with the lowest rated breaker available.
| All times are GMT -4. The time now is 10:44 AM. |