#1 |
Help New Addition Electrical Sub Panel/Load
I am in the process of building an addition. I am at the point of wiring the addition. I plan on using the space for a kitchen and small living room. I would like to run all the wiring and install a sub panel in the additions basement on my own. As far as providing power to the sub panel or updating the main service panel I will probably leave this for an electrician, who already stated he would evaluate my work. I want to make sure I install the correct size sub panel with the proper amps. I have questions about the electrical loads, if an updated service panel is required and suggestions with the installation of the sub panel. I want to make sure I am installing the electric components correctly.
Overall I plan on using a sub panel feeder breaker to power the sub panel, which will be placed 24’ from the service panel. I would like to power all the addition through the sub panel and not have to run any circuits back to the main service panel. I figure if I do upgrade to 200 amps, I will place a 100 amp feeder breaker in the main service panel to feed the sub panel. Any recommendations or concern would be appreciated. Thank you. Currently my house has a 100-amp service but I do not utilize all the amps. I have four open circuits and I will be taking out the 40-amp circuit for the range and placing it in the sub panel. Here is info about my set up. Currently the 100 amps services 1100 square foot home with a range, dryer, washer, refrigerator, gas furnace, and two-window ac’s. Electrical Load Calculation including new appliances. So the final electrical load would be: 1. 1591 square feet home. 2. 2 kitchen small appliance circuits 3. 1 laundry circuit. Permanent appliances will be: watts were found on appliances.
After doing calculations I come up with 89 amps. Does this sound right? Since the service panel is rated for 125 amps less 20% shouldn’t the service be adequate? Do I need to update the service panel to 200 amps? Here are the new circuits I will be adding. Total of 10 circuits.
#2 | |
MarginallyQualified
Help New Addition Electrical Sub Panel/LoadQuote:
The most common source of DIY problems is when they get "an idea" or believe their situation calls for X vs the far more common Y; and so forth. Avoid this. If you ever have a specific question... ask it. |
#3 |
Lic Electrical Inspector
Disposal? Well pump? Water heater?
All responses based on the 2011 NEC. If you live in New Jersey click To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. . All other states click To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. . Please check with local, county and state officials as laws may vary. Sizing motors To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. . Online motor calculator To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. . Online calculators To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. . |
#4 |
Licensed Electrician
What does your electrician say? I am on the fence. You are probably pushing a 100A service, but it doesn't appear that you NEED to upgrade to 200A. Do you ever plan on installing central air? That may help you make the decision.
Not a fan of the new layout.
Answers based on the National Electric Code. Always check local amendments. |
#5 |
The thing with a main breaker and the amperage rating of a subpanel is what *all* will you ever possibly have powered on AT THE SAME TIME.
You can have 400 amps of outlets, but only use 60 amps total at any one time, so a 100 amp main breaker would do fine (in that case). Or say somewhere like a wood shop where they have many workers and all the machines are all on at the same time, then the main breaker would need to exceed the total amperage of everything. And not everything in a kitchen would be powered on at the same time. I think the best test is Thanksgiving and a lot of people over. Lots of things on in every room of the house and lots of things on all at once in the kitchen. Maybe several people in the kitchen using various appliances at the same time - Grandpa's RV plugged into the house. Etc. So far as a subpanel, that can be determined by the largest breaker you can get for that to install in your main panel. Also the wire size can be very large and difficult to snake into the panel and to the subpanel, especially if aluminum. Copper of a large size can cost a small fortune, but will be smaller for the same amperage rating. Might want to go look at breakers for your main panel and the wire sizes for say 100 amps or 125 amps. Note this needs to be 4 wires for a subpanel - Hot, hot, neutral, ground. If your main panel is currently "crammed" with wires and there is no way you could fit additional large wires and a double breaker in there, that might be a consideration to upgrade and get a more "roomy" main panel. |
#6 | |
#7 |
Help New Addition Electrical Sub Panel/Load |
#8 |
I have four circuits open in the main service panel. I am just trying to figure out the best scenario for the additions electrical. Is the best scenario to upgrade the main to 200 amps and run all the new wire back 24' to the main service? Or should I install a sub panel in the addition and run the new wires to that? If I did run 10 circuits Back to the main panel can I run all the wires in one pipe of conduit? I am looking for suggestions. Thanks for the responses.
#9 |
E2 Electrician
Lets keep this as simple as possible, As stated, your 100 amp service is most likely adequate unless you want to add central air or a hot tub or other large appliance in the future...
If I was doing that job, I would run #2 SER AL. wire from the main panel to the sub-panel, fed with a 90amp breaker, I generally use 24 circuit / 125 amp panels. This should be more than generous for future circuits along with your addition.
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. |
#10 | |
#11 |
E2 Electrician
EMT can be used as the grounding conductor.
#12 | |
#13 | |
E2 Electrician
The sub panel will most likely be rated for 125 amps, but you're supplying it will a 90 amp breaker. And besides, if you do upgrade to a 200 amp service down the road, this will be all set and one thing you wont have to mess with, I would leave some wire slack at the existing panel so you have no issues with a bigger panel later on.
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. Last edited by stickboy1375; 07-29-2012 at 05:20 PM. |
#14 |
Thanks for the help stickboy.
#15 |
You could never use 6-3 for a 100A subpanel.
| Display Modes | |
| Electrical codes from 1970's -- Old work frustrations... | PirateKatz | Electrical | 3 | 03-18-2009 07:35 PM |
| Footing/Foundation for Addition | stubits | Building & Construction | 1 | 03-11-2009 02:43 PM |
| Electrical Box near Shower Valve | dasajame | Electrical | 3 | 07-07-2008 07:46 AM |
| 2 Prong Electrical | mjcongleton | Electrical | 10 | 04-16-2008 09:59 AM |
| to add an addition or not..... | elmorem@gmail.com | Building & Construction | 2 | 02-17-2008 11:43 PM |