Old 11-25-2012, 04:03 PM   #16
Help with new 220V sub panel circuit
I was kind of wondering, why is ok for the neutral and ground bus's to be bonded, connected together, in the main panel, but not in the sub panel? Just FMI.
darkbreeze is offline   Reply With Quote
Old 11-25-2012, 04:05 PM   #17
TTW
TTW's Avatar
Why isolate the neutral in a sub panel?...
The neutral is only bonded to ground at your service panel. At all other points throughout your house, there is no connection between the bare (or green) grounding conductor and the white neutral conductor. Under normal conditions, the grounding conductor carries no current. No current means there is no voltage drop along it, therefore anything "grounded" to this conductor is at the same potential (voltage) as ground. If you bond the neutral and ground at the sub panel, than stray currents from the neutral return could go thru the equipment ground on the electrical devices fed from this sub panel. If you isolate the neutral and ground at the sub panel, than any currents would go back to the main panel, and go to the service ground. The main panel is where the neutral and equipment ground should be bonded.
If you install a sub panel outside the building from the main panel, than you will need to drive a ground rod at this panel. A single branch circuit run to another building is not considered a sub panel.
TTW is offline   Reply With Quote
The Following User Says Thank You to TTW For This Useful Post:
darkbreeze (11-25-2012)
Old 11-25-2012, 04:06 PM   #18
I also wanted to just say thanks to those of you who are attempting to help me with this problem. I left messages on several other forums and several days later have received no response on any of them. So thank you for your help.
Old 11-25-2012, 04:06 PM   #19
Master Electrician
The TLM 1212 will accept GE THQL or THQP breakers. THQL are 1" in width and THQP's are 1/2" in width. It might be possible to replace several THQL's in the main panel with THQP's thus freeing up a space for a 2 pole THQP for the compressor.
brric is offline   Reply With Quote
The Following User Says Thank You to brric For This Useful Post:
TTW (11-25-2012)
Old 11-25-2012, 04:12 PM   #20
Here's a pic. You tell me, but I think everything is already reduced as far as it can go. Please let me know if I'm wrong.
Old 11-25-2012, 04:14 PM   #21
JuzRick's Avatar
Originally Posted by brric View Post
What do you consider an A/C disconnect? It is totally permissable to install a panel for 240 volt loads only. No neutral required.
Brric::: smart ***.. i never said install a subpanel. I asked if he had a combo panel outside he could utilize for the 30 amp brkr!
JuzRick is offline   Reply With Quote
Old 11-25-2012, 04:20 PM   #22
Master Electrician
Bottom right there are 2 THQP's. Above them there are 2 THQL's. The 2 THQL's could be replaced with THQP's and a 2 pole THQP could be placed between them.
Old 11-25-2012, 04:23 PM   #23
JuzRick's Avatar
Yes:: that can be done utilizing a 20/20 duplex brkr! Then you will have space for that 30 amp. I've done it. Learned it from a ME(Master Electrician). Passed inspections tooooo(if/when required)!!!!
Old 11-25-2012, 04:30 PM   #24
JuzRick's Avatar
Brric::: I will say here it is permitted. I know in some City(ies).. its not allowed. Not meaning isn't right. Some area's are stricter than others on certain situation- not saying that it is a safety violation! If pass inspection.. i consider it acceptable.
Old 11-25-2012, 04:30 PM   #25
If I read your original post correctly, this is a detached garage.
I assume it already has at least one circuit already feeding it.
You should be installing a larger subpanel and feed so that all of the garage requirements are served from the single subpanel.
Oso954 is offline   Reply With Quote
Old 11-25-2012, 07:00 PM   #26
Licensed Electrician
k_buz's Avatar
You do not have to run 4 conductors. If you use metal conduit, the conduit itself is the equipment grounding conductor and there is no need to run a ground.
Not a fan of the new layout.
k_buz is online now   Reply With Quote
Old 11-25-2012, 07:33 PM   #27
Electrical Contractor
I know that doesn't mean it was correct per code but I just want this to work for now, not worried about it being a licensed installation or being able to pass an inspection.
This right here tells me he's going to do what he wants.
If he has a circuit going to the garage, he can not run another!
Yes I am a Pirate, 200 years too late. "Jimmy Buffett"
Old 11-25-2012, 07:54 PM   #28
JuzRick's Avatar
Ok, so there are two bus bars in the sub panel. So as long as I run a neutral to the neutral bus in the sub, and a ground to the ground bus in the sub, I do not need to run any neutral wires from the sub out to the compressor, correct? Thanks
Well yes.. to have it match up. without it, the compressor wont start after plugging it in starting it.
The only exception you would have is on the ground side. the compressor will still start tho.
I still ground it... for you just may utilize the circuit for something else in the future. You just never know!
Old 11-25-2012, 08:49 PM   #29
" Euro " electrician
frenchelectrican's Avatar
I was reading thru on this one and I will address to the OP .,
Seince you mention you want to run the air compressour the only way you can do this in legit way is you have to ditch the exsting circuit and run a new circuit to the detached garage with new subpanel and one circuit for your air compressour and other circuits as needed in the garage.
There are few legit metholds you will have to use .,
A ) PVC conduit buried in the ground that have to be 18 inches deep and use 1.25 inch pvc with 4 conductors 3 X 6 awg conductors and 1 X10 gauge conductor ( 6 awg black, red , white and 10 awg green unless your code required the green to be #6 then do it.)
B ) Direct bural UF cable 6-3 UF cable that have to be 24 inches ( unless other depth per your local codes ) but you will need larger conduit due the 6-3 UF cable is pretty wide so therefore 1.5 inch is bare minum for riser for protection.
I rather just run all the way thru with PVC and with THHN/THWN conductors and be done with it.
Of course you will need two ground rods as well.
Again., keep the netural and ground seperated.
Merci,
Marc
Old 11-25-2012, 09:06 PM   #30
Master Electrician
I'm confused. Why won't the compressor start?
No neutral bus bar in 220v sub panel! to3032 Electrical 10 07-04-2012 03:29 PM
new circuit in sub panel jenrator Electrical 5 05-30-2011 07:45 AM
120 v circuit from 230 volt panel mills372 Electrical 3 09-07-2009 12:13 PM
Replace a service panel circuit breaker knockout? michigan_homeowner_2008 Electrical 6 05-22-2008 05:01 PM
Installing new circuit in panel - DIY? curls00 Electrical 18 03-13-2008 03:16 PM