Old 12-04-2011, 08:37 PM   #16
JOATMON
ddawg16's Avatar
Rewards Points: 820
Take a voltmeter and measure between neut and your two hots.....maybe turn something on like the dryer to see if there is a voltage change. Both of your hots should be within a couple of volts with the other....but if one leg jumps up in voltage and the other drops down....you have a problem with the transformer....
That one neut that is getting hot....do you know where it is going?
The Following User Says Thank You to ddawg16 For This Useful Post:
WillK (12-06-2011)
Old 12-04-2011, 08:38 PM   #17
I ask the impossible!
Rewards Points: 640
The screw bonds neutral to the chassis and both grounding bars are attached to the chassis.
I've done some more diagnostics:
With the main breaker off, the arcing stops.
With all circuits off and the main breaker on the arcing stops.
With everything off except the old main which is now a subpanel, arcing occurs.
With a few other things on, but the old main which is now a subpanel off, arcing occurs.
It seems that I get the arcing when any power is on, with no particular connection to any circuit.
I also made another attempt to tighten the bonding screw, it is now welded.
I know the info above is probably more useful diagnostic-wise than a video, but I have one which I'll be putting on youtube and posting a link shortly.
Please do NOT consider any "before" picture of my house as any kind of endorsement of any particular construction method. In fact, you should probably assume that if I post a "before" picture, I am posting it because I am soliciting advice on a proper replacement for one of MANY things done wrong by a previous owner.
WillK is offline   Reply With Quote
Old 12-04-2011, 08:40 PM   #18
Rewards Points: 640
The neutral that appears to be getting hot goes to the dryer. I think it's more likely it's getting hot due to proximity to the arcing, if the wire was heating up then the burn would not be isolated to the area near the neutral bar.
Before the kids went to bed I put the cover back on. When I ran my latest diagnostics, the cover was warm over where the arcing occurs.
And I haven't gotten out a voltmeter yet because it'll take some searching in the garage. Kids are asleep now so I will have time for that next.
Old 12-04-2011, 08:42 PM   #19
JOATMON
ddawg16's Avatar
Rewards Points: 820
We need voltage readings....but it really sounds like your return path is via earth ground and not your neutral....
WillK (12-06-2011)
Old 12-04-2011, 08:43 PM   #20
Sounds to me like something is shorting to ground in the old panel (subpanel).
Or an appliance or circuit connected to that panel.
(Hot shorting to ground.)
Billy_Bob is offline   Reply With Quote
Old 12-04-2011, 08:46 PM   #21
Licensed electrician
Rewards Points: 1,028
Is the bond screw still installed in the old panel?
Old 12-04-2011, 08:55 PM   #22
joed's Avatar
Rewards Points: 11,582
If it was a short to ground the breaker would be tripping.
It sounds to me like an open neutral causing the current to flow on the ground wire(from the panel not from a circuit) instead of the neutral.
Do you have a clamp on ammeter? Can you measure the current on the main service neutral and the main service ground wire. Try the main water line as well.
The Following 5 Users Say Thank You to joed For This Useful Post:
frenchelectrican (12-05-2011), Jim Port (12-04-2011), mpoulton (12-05-2011), Speedy Petey (12-04-2011), WillK (12-06-2011)
Old 12-04-2011, 08:57 PM   #23
Rewards Points: 640
I have removed the bond screw in the old panel.
Old 12-04-2011, 08:58 PM   #24
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
Reason I asked earlier was to clarify that the event is still occurring. Kb sparky is likely correct in his analysis. The only word of caution I'd like to convey is that your enclosure metal and ground wires are likely energized. From what source is yet to be determined. Becareful with this .. it may be more dangerous than you might think.
The discolored insulation on the dryer neutral at its connection point to the neutral buss bar lends itself to a high resistance return. As Joe said an amp meter would be your best friend at this point IMO ...
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
The Following 2 Users Say Thank You to Stubbie For This Useful Post:
mpoulton (12-05-2011), WillK (12-06-2011)
Old 12-04-2011, 08:59 PM   #25
Rewards Points: 640
I don't have a clamp on ammeter.
Did I mention the bond screw is now welded, and the arcing is continuous at this point?
Old 12-04-2011, 08:59 PM   #26
The breaker might not trip if it was a high amperage breaker (such as the breaker to the old panel). That screw might just appear as a normal load to that breaker. A heating element!
Old 12-04-2011, 09:05 PM   #27
Master Electrician
Rewards Points: 3,678
At this point it seems to me you need a professional on site ASAP or sooner.
brric is online now   Reply With Quote
The Following User Says Thank You to brric For This Useful Post:
WillK (12-06-2011)
Old 12-04-2011, 09:18 PM   #28
Rewards Points: 640
I've got my electrician coming out tommorrow afternoon, I spoke with him on the phone just now and that's about the sense of urgency he assigned to it when I described it as I had above. He also indicated that if they found it was with the PoCo he had contacts to break through the red tape and maybe get things to happen a little quicker.
Here's the video now:
Since the last work that was done, the meter was never re-sealed so I'm thinking maybe next I'll open it up and see if there's anything visually obvious. When I go to bed, though, I'm shutting everything down that I can... I'll have to leave things on like the kids lights, alarm clock, fridge, sump pump, fire alarms. Definitely shutting off electronics once I'm done talking to you guys... This laptop is going on battery.
Old 12-04-2011, 09:30 PM   #29
Rewards Points: 640
Pics of the meter socket top and bottom from just now, from my layman's perspective it doesn't look like a smoking gun. I'm thinking I'll go through the exercise of calling this in to the PoCo now as well. The arcing is very unsettling.
I'll also see if I can shut off the main breaker and get a jumper in between ground and neural bars using light from the laptop to work. At least maybe I can eliminate the arcing.
Help! Glowing spot at bonding screw-meter-socket-bottom-04dec2011.jpg   Help! Glowing spot at bonding screw-meter-socket-top-04dec2011.jpg
Old 12-04-2011, 09:35 PM   #30
liscenced electrician
Rewards Points: 538
I think that screw is what bonds the neutral bar to the neutral service conductor and its making a crap connection causing it to heat up. Take that screw out and wire brush it, apply some de-ox and torque it back down.
Nevermind. Looks like that screw bonds the can. There shouldn't be any current on it, but either way, the heat is from a poor connection
jimmy21 is offline   Reply With Quote
Robertson tip stuck in screw djgrant General DIY Discussions 4 07-05-2011 05:18 PM
Stuck Screw IceTreay General DIY Discussions 11 09-09-2010 02:56 PM
gas line vs screw wobblybowl Plumbing 5 05-27-2009 11:49 PM
Allen screw and copper pipe? dolvio Plumbing 1 02-09-2009 07:38 PM
Wire size for 300watt trans, 3 way 100ft Al the Diy guy Electrical 16 03-22-2008 09:46 PM