Help! Glowing Spot At Bonding Screw - Electrical - DIY Chatroom Home Improvement Forum
Old 12-04-2011, 03:02 PM   #1
I ask the impossible!
Rewards Points: 660
Help! Glowing spot at bonding screw
So I heard a faint sound that could have been either a sizzle or a squirrel on the roof. Since a quiet house with a 5 year old girl, a 6 year old boy and a high strung redheaded wife is something that only happens when everyone is asleep, I decided the best way to figure out if it was electrical was to take off the cover from my main panel.
Sure enough, I saw a little spot glowing on the side of my bonding screw. By the time I took the picture, the spot had cooled down to the point it isn't glowing enough to capture in a photo. However the label next to the spot is burnt and the neutral wire for the dryer shows signs of having overheated.
I have 2 questions:
One thing that seems to be needed is to ensure the bonding screw is tightenned properly, is there any reason to be concerned about doing this (I'd otherwise assume the answer is no, but with enough current to cause metal to glow where there should be no current flow, I don't want to assume it's safe.)
Second question: What could cause this?
For those that don't remember, I installed this panel myself and it was done under permit with very close scrutiny under inspection. All the circuits in this panel are new, my POCO moved the service entrance to this panel just before labor day after which a tree fell on the service entrance.
For some reason I'm having difficulty posting pics, but it's a 200A Homeline panel and I'll get back to post pics later when I Can.
Please do NOT consider any "before" picture of my house as any kind of endorsement of any particular construction method. In fact, you should probably assume that if I post a "before" picture, I am posting it because I am soliciting advice on a proper replacement for one of MANY things done wrong by a previous owner.
WillK is offline   Reply With Quote
Old 12-04-2011, 03:34 PM   #2
Rewards Points: 660
I have the photos attached now.
The bonding screw was originally green.
I've tightenned the bonding screw a quarter turn but it's still acting the same. I'm pretty sure I probably originally went so far as putting a torque wrench on the screw.
Also I've shut off the breaker for the garage and dryer, but that had no effect.
Could I be getting current jumping from one of the hot wires to the neutral in the service entrance? After the tree fell, I had complained about how the POCO fixed it, but they said it was fine. Their fix put the hot wires under tension.
Help! Glowing spot at bonding screw-glowing-spot-bonding-screw.jpg   Help! Glowing spot at bonding screw-main-panel-question-04dec2011.jpg
Old 12-04-2011, 03:50 PM   #3
Rewards Points: 6,652
Power surge most likely, somewhere on the same leg that your house is on.
Old 12-04-2011, 03:58 PM   #4
Master Electrician
Rewards Points: 3,824
Where is the grounding electrode conductor??????????
And what type of electrode(s) do you have?
brric is online now   Reply With Quote
Old 12-04-2011, 04:52 PM   #5
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
When you say you turned off the dryer breaker and garage breaker and it didn't change anything are you saying that the bonding screw is continuing to glow ?
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 12-04-2011, 05:09 PM   #6
Rewards Points: 660
The panel has a GEC connected to the ground bar on the right hand side and it connects to two 5/8" ground rods.
It does not glow continuously. It is arcing intermitently. It stopped for a little while when I asked my neighbor if he'd stop by and look at it, but it has since restarted.
Old 12-04-2011, 05:11 PM   #7
Rewards Points: 660
Yes. The arcing it was doing intermitently did not seem to stop when I did anything like shutting off the garage and/or dryer circuit breaker, and it did not change either with shutting off bathroom lights, christmas tree or anything else I tried.
I had been noticing that the bathroom lights would dim for a second here and there in the morning, but I never noticed anything else. Today now that I noticed the ground bonding screw, I'm noticing that when it arcs that a slight dimming of any incandescent lights in the house can be seen.
Old 12-04-2011, 05:15 PM   #8
Rewards Points: 1,500
Flip off all branch circuit breakers. Then turn on breakers one at a time or a few at a time. Can you isolate the glowing spot to just one breaker? What appliances does that breaker serve?
Next, unplug everything except for a few incandescent lights. Remove the bonding screw. Turn on the breakers for the incandescent lights. Go upstairs and turn individual lights on and off. Do other lights dim or brighten? Try plugging in the incandescent light into different circuits.
With the bonding screw removed and a few incandescent lights turned on, and all 240 volt circuits (double breakers) flipped off what is the voltage from hot to hot, and from hot to neutral and from neutral to ground in the panel. Write it all down.
By the way, hot shorting to neutral up on the line going to the utility pole will probably not cause the glowing spot you described.
The Following User Says Thank You to AllanJ For This Useful Post:
WillK (12-06-2011)
Old 12-04-2011, 05:35 PM   #9
Electrical Contractor
kbsparky's Avatar
It sounds like you have quite a load imposed on the connection between the grounded enclosure of your panel, and the neutral wires.
I see from your photo that you have a separate equipment grounding bar present. You may have back-feeding juice coming in from your water mains, if you are bonded to a municipal water system.
OR your neutral line outside could be bad, and all your juice is returning VIA your water pipes. Either way, you should call the power company.
Is this a sub-panel, or your main service panel (It should be your main service panel, considering there is a bonding screw present)?
Since you have separate equipment grounding bars, AND you are dealing with the main service panel, start by installing a jumper wire between them. That should eliminate the potential between the neutral and the enclosure.
-KB
The Following 4 Users Say Thank You to kbsparky For This Useful Post:
frenchelectrican (12-04-2011), Jim Port (12-04-2011), mpoulton (12-05-2011), WillK (12-06-2011)
Old 12-04-2011, 06:06 PM   #10
joed's Avatar
Rewards Points: 12,440
Since there should never normally be any current flow through the bond, this is the best advice you have received. Loose neutral connection on your or a neighbour's service was my first thought.
The Following 4 Users Say Thank You to joed For This Useful Post:
frenchelectrican (12-04-2011), mpoulton (12-05-2011), Speedy Petey (12-04-2011), WillK (12-06-2011)
Old 12-04-2011, 06:53 PM   #11
Rewards Points: 660
The arcing at the bonding screw is observed in the main service panel. I originally installed this as a sub with the intent of moving the service entrance such that this panel became the main. Late August is when the POCO completed the move of the service entrance.
My longer term intent is to move all the old circuits from the original main panel, which is now acting as a subpanel. The old work is suspect, but the worst has been replaced.
At any rate, after the PoCo connected, a tree fell on the service entrance. We didn't lose power. The Poco disconnected and reconnected over top of the fallen tree. But the service drop hung too low to the garage, so I called and they came out and pulled it tighter to gain clearance, and reconnected. Then after that I had an electrician replace a broken insulator in the service cap, so that would be a third time the service connection at the top of the service mast was redone.
At any rate, I'll try shutting off more breakers after kids go to bed. I've been meaning to disconnect the old main which is now a sub since that would isolate a big chunk, but the TV and first floor lights run off that and the kids would start shrieking without TV or lights.
Old 12-04-2011, 06:54 PM   #12
Rewards Points: 660
And the same electrician that replaced my service cap insulator replaced my neighbor's main panel, about the same time the other half of my tree would've landed on his service entrance (actually it fell while they had it down.)
Old 12-04-2011, 06:57 PM   #13
Rewards Points: 660
One note I wanted to add: Same time we got the service move, PoCo upgraded the neighborhood including us to digital meters. I was wondering how well this might serve in the PoCo being able to detect a problem remotely if I was to call?
Old 12-04-2011, 07:05 PM   #14
Not really. They operate in the same sense that a Ted5000 does, but only update in a lesser rate than the Ted does.
Old 12-04-2011, 07:19 PM   #15
If an appliance (such as the dryer) were to have a hot shorting to ground, how would that hot current get back to neutral?
Only via that bonding screw?
Do you have 2 ground bars?
Do they both connect to ground via heavy gauge ground wires? Or is one only connected to your ground and to neutral via that screw?
Billy_Bob is offline   Reply With Quote
Robertson tip stuck in screw djgrant General DIY Discussions 4 07-05-2011 04:18 PM
Stuck Screw IceTreay General DIY Discussions 11 09-09-2010 01:56 PM
gas line vs screw wobblybowl Plumbing 5 05-27-2009 10:49 PM
Allen screw and copper pipe? dolvio Plumbing 1 02-09-2009 06:38 PM
Wire size for 300watt trans, 3 way 100ft Al the Diy guy Electrical 16 03-22-2008 08:46 PM