Help With 20A 240v Receptacle - Electrical - DIY Chatroom Home Improvement Forum
Old 03-26-2009, 06:55 AM   #1
Rewards Points: 156
Help with 20A 240v receptacle
I had one of these in an outlet under a window in my house. I removed the wire all the way back to a junction box and pulled it out. Best I can tell, there isn't actually anything else on this circuit. It's yellow #12 romex from the panel to the junction box and then it continued on as a grey fabric-style cable to the outlet -- that was the section of wiring that I ripped out.
I'm assuming this is just a standard 20 amp circuit so I could potentially tie in new romex and use the empty outlet box for a normal outlet on a 20amp circuit now right?
jayp is offline   Reply With Quote
Old 03-26-2009, 07:41 AM   #2
Yes, all you need to do is remove the white from the breaker and attach it to the neutral bus, remove the black tape on the white. You can replace the breaker with a single pole and install a blocker if you want. You need to continue this circuit with 12 awg if you keep it at 20 amp. You need a 15 amp breaker if you extend it with 14.
rgsgww is offline   Reply With Quote
Old 03-26-2009, 08:01 AM   #3
Rewards Points: 894
Jay;
What drawing app are you using to create your drawings?
Looks really professional
FW
Ultrarunner2017 is offline   Reply With Quote
Old 03-26-2009, 09:15 AM   #4
Rewards Points: 156
haha
I stole it off another website. haha
Old 07-07-2011, 09:56 AM   #5
Electrical Estimator
2008 Code Change
Per the 2008 Code changes, you can Not us a Neutral (White) wire to carry power to device. Per the new code changes, they are making us run 12/3 Romes/MC wire which has a Red (Hot), Black (Hot), White (Neutral), and ground in it. Just a heads up if this is getting inspected!
garber2007 is offline   Reply With Quote
Old 07-07-2011, 10:19 AM   #6
Master Electrician
Rewards Points: 3,874
That is TOTALLY incorrect. You are referring to 120/240 volt circuits that require an insulated neutral.
brric is offline   Reply With Quote
Old 07-07-2011, 11:08 AM   #7
Mis-Information
I apologize for not making my self clear. When you run a 240V circuit, we are not allowed to use the Neutral as a current carry conductor, even if we tape up the wire with black tape, to show that it is not a neutral. Is that better, brric?
Old 07-07-2011, 11:12 AM   #8
Licensed electrician
Rewards Points: 1,630
Could you please cite the NEC article that prevents this? The white conductor is allowed to be re-identified as a hot in a cable type assembly.
Old 07-07-2011, 11:18 AM   #9
Master Electrician
See post #8. It is not a neutral to begin with.
Old 07-07-2011, 11:41 AM   #10
The neutral is a current carrying conductor. It is returning the unbalanced current from the ungrounded legs.
Old 07-07-2011, 11:54 AM   #11
Well, this conversation is getting pretty interesting...I am going to set down with the Code Book tonight. I work for an commercial/industrial/residential contractor and the guys I work with have recently been telling me that I cannot use the neutral for any thing other than a neutral conductor because of the code. I am also not sure if this is something that is coming out in the 2011 version, or not. Let me know if you guys see anything that has changed in 2011 if you get a chance. Look forward to reporting if I am wrong or not tomorrow or the next day! Got to get back to work know! Thanks for debating with me about this!
Old 07-07-2011, 01:02 PM   #12
Master Electrician
We are not talking about a neutral. The point is a 240 volt circuit may be supplied by a cable assembly consisting of a black and white conductor when the white conductor is reidentified as a non-grounded conductor. NEC 2008 Article 200.7(C)(1).
NEC 2011 Article 200.7(c)(1).
The Following 2 Users Say Thank You to brric For This Useful Post:
frenchelectrican (07-07-2011), Jim Port (07-07-2011)
Old 07-07-2011, 09:07 PM   #13
Electrical Contractor
kbsparky's Avatar
You must be talking with a bunch of Canadians. Up there, they have to use different romex that has a black and red in it (no white)for 240 VOlt circuits....
-KB
Old 07-07-2011, 09:14 PM   #14
Master Electrician
Could be. Says he's from Ohio.
Old 07-11-2011, 06:21 AM   #15
Rewards Points: 156
Guys, this post was from 2009!
Isolated Ground Receptacle Bocolo Electrical 40 01-23-2012 02:44 PM
Wiring A Ceiling Fan, Receptacle, and Outside Light merlin6984 Electrical 9 03-26-2009 09:52 PM
Receptacle Rating question Ultrarunner2017 Electrical 19 12-20-2008 06:20 PM