Help, 110 V from each leg but no 220 between legs
My central air conditioning air handler, with electric heat, suddenly will not run. I measured the supply voltage to the breaker at the air handler and there is 110 volt from the black wire to ground and 110 volts from the red wire to ground. No voltage registers on the meter when measuring between these black and red wires.
I checked the meter on another 220 volt circuit and it works. Any ideas?
petergun1 is offline   Reply With Quote
Old 12-25-2011, 03:16 PM   #2
Rewards Points: 6,652
That is what you should be getting. If the unit is not running, and there is voltage, next thing is to check to see if the contactor, when pushed to close the circuit will start it, along with checking the capacitor for bulging. The cap looks like a small soda can, and would be in the same area, behind the access panel.
The Following User Says Thank You to gregzoll For This Useful Post:
petergun1 (12-25-2011)
Old 12-25-2011, 03:22 PM   #3
Civil Engineer
Rewards Points: 4,938
Whoa Gregzoll, if that is a 240 volt circuit (as OPS states) he should be getting 240 volts from one hot to the other, certainly not zero. The only way I see you getting zero volts hot to hot on a 240 volt circuit, and 120 hot to ground on each leg, is if you were pulling 120 volts for each hot off the same bus bar at the panel, in which case that is exactly what you would read, but the unit would never have worked. Perhaps one of the experienced electricians can answer this puzzle. You didn't switch out the breaker by any chance?
The Following User Says Thank You to Daniel Holzman For This Useful Post:
Old 12-25-2011, 03:27 PM   #4
Thanks Daniel, I did not catch the zero across legs. Could just be a bad disco outside. I wonder that now that you mentioned it, if they may have a tandem vs a dual pole, or one of the panels, that if you do not place the breaker in one of the right spots, you get the same phase off the panel. That would make more since on the 110 on both legs.
Old 12-25-2011, 03:28 PM   #5
MarginallyQualified
Rewards Points: 2,464
Originally Posted by petergun1 View Post
I measured the supply voltage to the breaker at the air handler ...
go back to the panel and check what you have there
Any ideas?
something very fundamental is seriously out of whack.
hth
The Following User Says Thank You to TarheelTerp For This Useful Post:
Old 12-25-2011, 03:29 PM   #6
Rewards Points: 3,256
Where exactly are you reading these voltages? It is not uncommon to read backfed voltage if you have a leg open. Do you have fuses inside your air handler? You mentioned a breaker, is that the panel breaker?
zappa is offline   Reply With Quote
The Following User Says Thank You to zappa For This Useful Post:
Old 12-25-2011, 04:09 PM   #7
joed's Avatar
Rewards Points: 13,696
One of the hots is open. You are reading the 120 volts on the dead leg through a backfeed from the AC.
Several possibilities. Assuming you have not been working in the panel and this was functioning previously.
1. The breaker is bad.
2. The breaker has a bad connection to one bus.
3. One of the wires in the cable has come loose.
4. There is fuse in the AC disconnect that one of them has blown.
If you have been working in the panel
1. Tandem or mini breaker used instead of a double pole 240 breaker.
2. In some panels the double pole breaker can be installed so both legs are on the same bus.
The Following User Says Thank You to joed For This Useful Post:
Old 12-25-2011, 04:24 PM   #8
Smile
Let me thank everyone that replied. The zero voltage was measured at the air handler breaker. The panel breaker did show 220 volts, so I went back to the air handler breaker and removed two wires that were wired to the supply side of the breaker. These wires lead outside to the air conditioning unit. The heater now works and I will have to figure out what those wires supply in the next couple of days -- it's raining right now.
A little info: I live in a small southern Mississippi town where until four years ago building regulations were almost none existent. The process entailed paying ten dollars for the permit, no one ever followed up. Essentially you could do whatever you wanted. Who know what I will find when I open the side of the air conditioner.
Again, thanks for the quick and valuable replies.
The Following User Says Thank You to petergun1 For This Useful Post:
zappa (12-25-2011)
Old 12-25-2011, 04:32 PM   #9
Sounds like the feed to the outdoor unit. I wonder what your original problem was and why it fixed itself.
Old 12-25-2011, 06:03 PM   #10
dmxtothemax's Avatar
Rewards Points: 5,598
Two options explain your syptoms -
You have lost one leg !
The voltage you are measuring with the meter,
could well be a back feed voltage !
or
Both hots are coming from same phase/hot.
What has changed recently ?
dmxtothemax is offline   Reply With Quote
Old 12-25-2011, 06:19 PM   #11
I'm Your Huckleberry
Rewards Points: 2,270
not if his heater is currently working, it's not back feeding. it's an electric air handler, requires 240 volts for the electric heating elements and the blower to run simultaneously.
Thanks.
Doc Holliday is offline   Reply With Quote
Old 12-25-2011, 06:23 PM   #12
That is your 240 volts to your condenser. You may have a single pole contactor in the condenser which means one leg is always drawing hot and could be the problem. You can change that contactor to a double pole so no hots are drawing unless cool is calling. You now have heating but no cooling.
The right way is they are supposed to be on individual breakers. Most likely the outside condenser on a double 30-50 amp and the inside air handler being a double 60.
You have on or two sets of breakers in the air handler? Might be a double 60 and a double 30.
Thanks.
Attaching under table shelf to legs PCMLR Carpentry 2 04-01-2011 04:10 AM
shimming vanity legs ksspears Kitchen & Bath Remodeling 12 12-12-2010 12:46 PM
Supporting legs on Whirlpool! moosejohnson Plumbing 2 05-28-2009 04:24 PM
Voltage Difference between legs mimitche Electrical 13 05-02-2009 09:37 AM
Modern cabinet legs? Joony Carpentry 3 07-30-2008 05:36 PM