Heating Up - Electrical - DIY Chatroom Home Improvement Forum
Old 05-26-2009, 04:20 PM   #1
300zx's Avatar
Heating up
Can anyone tell me if AFCI Breakers should get warmer than regular breakers. They are Ch Cutler Hammer.All the breakers are about 85 The AFCI Breakers Are 107. Did a amp test 0.8 amps on all three AFCI'S. Thank you
300zx is offline   Reply With Quote
Old 05-26-2009, 05:11 PM   #2
Is the surface area of your AFCI less than that of the others?
The one 20A CB that I autopsied had a 2w resistor in it for the thermal trip. If 2w causes a 85-30 rise above amb. then the thermal resistance is 28C/w. For the same thermal resistance the AFCI would be using up 107/28 = 4w. That's probably a reasonable power consumption to run all the circuitry inside one of these.
Old 05-26-2009, 05:23 PM   #3
300zx's Avatar
Post
Yoyizit. Thank you for fast reply. I think i found a reply on another forum this is what it said -
Yes, that's completely normal. The manufacturers say that they may have up to a 40 degree temperature rise over ambient. Sorta throws you for a loop, doesn't it?
For this reason, some installers prefer to leave a blank space or a regular breaker between groups of AFCI breakers. Keeps them from heating each other up so much. Give a little room in between to cool off. This isn't expressly required by any manufacturer, but some installers consider it good practice.
Old 05-26-2009, 05:32 PM   #4
At rated current; you were drawing way less than that, which throws off my thermal resistance calc's.
Can you imagine the case of a CB at 70C?
"burned in 30 sec at 54C
5 sec at 60C
1 sec at 71C"
Heating Unit farooq Plumbing 2 07-18-2008 05:23 PM
Electrical consumption of baseboard heater CowboyAndy Electrical 7 03-24-2008 07:27 PM
Central Heating Frustration SassySue General DIY Discussions 4 11-29-2007 06:46 AM
Trane XE80 Heating Question, Please help!!! Stephen1977 HVAC 3 01-30-2007 06:34 PM