Heater wiring and breaker size question
I have an electric heater I want to install in my garage. It says 208/240 volts, 1phase, 0.22 amps, 60hz. I'm just confused because it says 0.22 amps, not 22 amps. Does this mean it draws 22 amps and I need a 30 amp breaker with #10 wire?
Also, is this any kind of timer switch that could be used with this? I want something like in the picture below. The only ones I can find are 110v.
Tmb9862 is offline   Reply With Quote
Old 12-24-2009, 02:01 PM   #2
Remodeling Contractor
You will need to check the rating carefully. What is the output rating of this unit? Seems like a 2P30 requirement would be likely. The switch needs to be rated to handle the same rating. You can use a 110V switch to break only one leg to the heater, but some local codes do prohibit this.
Old 12-24-2009, 02:07 PM   #3
Rewards Points: 79
Their isn't much more information then I gave on it. It has an area for minimum supply circuit ampacity but the area is left blank. It has a section saying "Controls" 208-240 V.A.C, 1PH, 60hz
Old 12-24-2009, 02:10 PM   #4
Rewards Points: 1,016
Yeah, I think they mean 22 amps - how many watt heater? Does it have a plug or hardwired - if plug you can tell from the plug.
I just went through installing very similar in my workshop/garage. Mine was 5600 watts / 24 amps so I installed a 30 amp breaker and #10 wire with a 30 amp double pole wall switch to turn it on/off.
I also wanted a countdown timer switch as you depict, but was unable to find one to handle to 30 amps (Intermatic does have 240 volt but lower amps, and with time to 6 hours). Suggested was to install a contactor (relay) to power the heater and activate the contactor with countdown timer now with the lower current requirement. I have not figured out the bits and pieces to do this - was also suggested to go to a electrical supply to get what is needed.
Old 12-24-2009, 02:16 PM   #5
you can find a timer to handle this at www.smarthome.com
Old 12-24-2009, 02:24 PM   #6
I had looked there before, and just did again. I don't see a double pole with 30 amp capacity - I do see a single pole 20 amp (http://www.smarthome.com/4255W/Multi...6260M-W/p.aspx)
Old 12-24-2009, 03:02 PM   #7
CodeEnforcer
HIVOLT's Avatar
Rewards Points: 99
FD60MWC Intermatic this switch can be used on electric heater because it will not be running continuously.
HIVOLT is offline   Reply With Quote
Old 12-24-2009, 03:31 PM   #8
try calling.. May not be posted on the site.
Old 12-24-2009, 04:20 PM   #9
That switch is rated at 240 volt 10 amp and is single pole - help me understand how can this can work or be ok for this application?
Here is a link to all such countdown timers at Intermatic - there are a few that are double pole, but 240 volt 10 amp max.
http://www.intermatic.com/products/t...%20timers.aspx
Old 12-24-2009, 06:20 PM   #10
CodeEnforcer
HIVOLT's Avatar
Rewards Points: 99
You are correct I posted the wrong catalog number. You would nee a DPST timer which is FF412H Intermatic. Although it is rated at 10A it will work.
Old 12-24-2009, 07:14 PM   #11
I still need help in understanding how a 10 amp capacity timer/switch can be used in a 30 amp circuit?
Old 12-26-2009, 09:04 AM   #12
Master Electrician
JohnJ0906's Avatar
It won't - at least not for very long.
John from Baltimore
One Day at a Time
"Experience is what you get when you were expecting something else"
"The bitterness of low quality lingers long after the sweetness of low cost is forgotten"
JohnJ0906 is offline   Reply With Quote
Old 12-26-2009, 03:27 PM   #13
" Euro " electrician
frenchelectrican's Avatar
IIRC Intermatic did not have legit 20 or 30 amp double pole timer at all.
It will work but you will burn up the timer no question ask due the timer is rated for 10 amp at 240 volts so try run 22 amp thru the timer you will burn up the concats due the timer is rated for 2400 watts and you are try to run 5,280 watts thru that timer and it will burn up pretty fast.
Really you can use standard timer and get a high current relay or contractor that should take care all the issue you are facing it.
Merci,Marc
Recessed lights, wiring, breaker buzzing, etc diyguy999 Electrical 3 12-21-2009 01:10 PM
Quick wiring question with HVAC Gjtrafl Electrical 4 06-25-2009 02:03 PM
wiring a 240V baseboard heater 777 Electrical 10 05-17-2009 10:47 AM
Wiring to a water heater bvsmith_1974 Electrical 3 09-03-2008 03:32 AM
Breaker question mrsql Electrical 11 02-21-2008 04:28 PM