Old 06-10-2008, 08:20 PM   #16
You do not wire the refe to a gfci in your kitchen.. What the problem is you should not put one in the garage. I have not done my update yet but you would not wire a washing machine to a GFCI,you would use a single recp. I'll have to check my code but I think you are wrong.
pothiel is offline   Reply With Quote
Old 06-10-2008, 09:29 PM   #17
Power Gen/RS Engineer
Rewards Points: 566
<-- Picture of Jimmy laying next to his chair laughing and spitting up.
Well, now, there's what's right and what's right and never the twain shall meet.
BigJimmy is offline   Reply With Quote
Old 06-10-2008, 10:23 PM   #18
Electrician
Like I have nothing better to do than make stuff up all night.
chris75 is offline   Reply With Quote
Old 06-10-2008, 10:55 PM   #19
Electrician
If the washing machine was located in a bathroom it would be GFCI protected.
Old 06-11-2008, 12:25 AM   #20
Rewards Points: 1,088
I have found also that depending upon installation technique (backstab vs. screwdown), the backstab can handle less current and more likely to melt the outlet.
handy man88 is offline   Reply With Quote
Old 06-11-2008, 06:33 AM   #21
I'm not saying you make stuff up. I just know that is not a good idea to put this kind of an appliance on a GFCI. Now an acfi is another story. GCFI have there place.
Old 06-11-2008, 06:55 AM   #22
Electrical Contractor
wirenut1110's Avatar
Rewards Points: 510
Send a message via AIM to wirenut1110
I believe this is just because a back stabbed connection eventually becomes a loose connection. Which causes arcing which increases heat and so on. Which is why I never do it, won't let my people do it and never recommend it. Makes for an easy service call though.
wirenut1110 is offline   Reply With Quote
Old 06-11-2008, 06:55 AM   #23
When is fishing season?
CowboyAndy's Avatar
Good idea or not, the 2008 NEC is requiring things like that to now be GFI protected. PERIOD.
With the NEC, you don't get to skirt by a code just because you don't think its a good idea... just like inspectors can't make up codes just because they think its a good idea.
Section 210.8 (A)
Ground-Fault Circuit Interrupter Protection
for Personnel; Dwelling Units.
The exception numbers (1) and (2) have been removed and GFCI protection is now required for most receptacles in unfinished basements and in garages and accessory buildings that have a floor located at or below grade level not intended as habitable rooms and limited to storage areas, work areas and areas of similar use.
(1) Receptacles that are not readily accessible
(2) A single receptacle or a duplex receptacle for two appliances located within dedicated space for each appliance that, in normal use, is not easily moved from one place to another and that is cord and plug connected in accordance with 400.7(A)(6), (A)(7) or (A)(8).
Analysis of Change:
Lack of “accessibility” of receptacles in these areas is no longer seen as reason to exempt them from the protection provided by ground-fault circuit interrupter protection for personnel. Similarly, the exception for receptacles in dedicated spaces for appliances in garages and accessory buildings has been removed. The expanded use of GFCI receptacles in these applications will necessitate boxes having larger capacity in some cases. Exception number (3) was retained for a receptacle supplying a permanently installed fire alarm or burglar alarm system.
I DON'T OWN MY HOUSE...
MY HOUSE OWNS ME!
CowboyAndy is offline   Reply With Quote
Old 06-11-2008, 07:40 AM   #24
There were a ton of changes in the 2008 NEC. Like I stated I have to check the code. Thanks for the input. Does this include the kitchen circuit for appliances.
Old 06-11-2008, 07:50 AM   #25
I think I read in the instructions that a 20 amp outlet can handle 12 gauge if you screw it down, but only 14 gauge (15 amp breaker) for back stab is recommended.
There is a lot less contact between the copper and the backstab method, in addition to the exposed copper touching the plastic casing.
Old 06-11-2008, 09:48 AM   #26
Rewards Points: 566
Please explain your reasoning.
Old 06-11-2008, 11:55 AM   #27
Because when refe's age they sometimes trip GFCI circuits and you lose all of your food. The code states that you can not install circuits without GFCI in unfinished basements etc. etc. you still wire the refe to a non GFCI in the kitchen because of this. You may have no problems with a circuit that is GFCI protected but why take the chance of losing your hard earned money on a circuit that does not require this protection. GFCI are great for personal protection. They are not so good for washing machine refe's freezers etc. The code change is going to be for all future wiring and does not include existing circuits.
Old 06-11-2008, 12:23 PM   #28
CowboyAndy's Avatar
Of all the things that can be problematic, the refer is the least of my concerns, IMO. We open our refer many times a day. My wife and kids know to let me know if the light is not on. I will usually verify the fridge is running before replacing the bulb.
It is things like chest freezers that are more of a worry, as they get used less often.
But the bottom line is if a given area has adopted the 08 code and doesnt ammend that requirement, then you HAVE to use GFI on the fridge and freezers, etc.
MY HOUSE OWNS ME!
Old 06-11-2008, 12:42 PM   #29
The code states that in the kitchen it is not required. 210.8(A)6 GFCI for all counter top. The 2008 NEC handbook gives a better example.
Old 06-11-2008, 01:42 PM   #30
Rewards Points: 566
It's a rarity that I disagree w/ Wirenut and this is no exception. If the receptacle was listed for this type of connection, there is no way on earth that it would offer a higher resistance by design. The two types of connections are meant to be equivalent although most people who are "in the know" won't use them (back stabs).
Freezer tripping GFCI davidclements Appliances 58 07-03-2015 06:46 AM
New GFCI Breaker Tripping w/ 3-way Flourescents BigJimmy Electrical 8 12-29-2008 03:29 PM
Hot Tub GFCI Grounding Question kearnak1420 Electrical 3 04-30-2008 06:48 PM
20 Amp Breaker tripping with GFCI panhandlion Electrical 7 12-12-2007 09:59 PM
GFCI questions 5circles Electrical 4 11-05-2007 09:24 PM