Has Anyone Seen An SE Cable Style U With No Red Line? - Electrical - DIY Chatroom Home Improvement Forum
Old 05-13-2013, 07:59 AM   #1
Has anyone seen an SE Cable Style U with no red line?
We tried to install our oven yesterday and discovered that both hot wires are solid black. Does anyone know how we can tell which one should have the red line?
kbybucks is offline   Reply With Quote
Old 05-13-2013, 08:02 AM   #2
Licensed Pro
Doesn't matter, both are hot.
Old 05-13-2013, 08:08 AM   #3
So if we're connecting them to the oven, they're interchangeable? The instructions said to connect the red one to the right side and the black one to the left side.
Old 05-13-2013, 08:11 AM   #4
Licensed Pro
correct
The Following User Says Thank You to HouseHelper For This Useful Post:
kbybucks (05-13-2013)
Old 05-13-2013, 09:49 AM   #5
Remodel and New Build GC
MTN REMODEL LLC's Avatar
Rewards Points: 2,854
Each maufacturer colors their cable a little different... your stove/oven just assumed one hot was black, one was red (traditional marking). As long as you've got both hots, right or left doesn't matter
MTN REMODEL LLC is offline   Reply With Quote
Old 05-13-2013, 09:58 AM   #6
Rewards Points: 160
If you installed an SE cable for your oven, you have created a code violation and should install the correct cable. If the SE cable was already present, you do not need to replace it.
The Following User Says Thank You to J. V. For This Useful Post:
MTN REMODEL LLC (05-13-2013)
Old 05-13-2013, 10:02 AM   #7
Licensed electrician
Rewards Points: 1,630
Is your oven straight 240 volt and not 120/240? If it is 120/240 you may have the issues JV brought up above.
Old 05-13-2013, 10:31 AM   #8
Jim and JV... Could you explain further.... I've never really understood the difference and application of :
1) The differnce in SE (r) and SE (u) for service entry
2) And why you don't / shouldn't use SE for an appliance run (apart from being aluminum)
Don't both SER and SEU come with the different current carring conductors and ground wire in most all sizes and necessary configurations.
Thanks for any help understanding
Peter
Old 05-13-2013, 11:21 AM   #9
SE-U is two insulated condcutors with a third spiral wrapped conductor. It is normally used for servicee entrance cable. Normally the bare is used for the neutral in a service application.
SE-R has three or more insulated conductors and a bare grounding conductor. Two hots, a neutral and a ground. A stove with both 120 and 240 volt requirements could use Se-R. Se-R would also be used to supply a subpanel.
Both cables can be aluminum or copper.
Old 05-13-2013, 12:20 PM   #10
This is an existing power supply and we haven't moved or extended it.
This is what it says for electrical requirements:
Power Supply Connection Location: Rear Bottom Left
Connected Load (kW Rating) @ 240/208 Volts: 13.7/11.3
Voltage Rating: 240V/208V/60Hz
Amps: 57.1/54.3
Minimum Circuit Required (Amps): 50
Now we're worried because the circuit it's on is a tandem 40 amp (each of the small breakers says 40). We aren't sure if that means it's 80 amps total or 40 and the range requires 50, so I think we might be calling a pro in.
Old 05-13-2013, 01:10 PM   #11
Licensed Pro
Amps: 57.1/54.3
You need to determine what wire size the SE cable contains, and if it is copper or aluminum.
Old 05-13-2013, 01:15 PM   #12
The 40 on the breaker is a 40 amp circuit. You do not add the handles to get an 80.
Your current breaker is too small according to the requirements posted.
Do not change the breaker without knowing the wire size and ampacity.
Old 05-13-2013, 01:18 PM   #13
Amps: 57.1/54.3
Its 40
Old 05-13-2013, 01:37 PM   #14
Thanks everyone. I think this is going to be more advanced than what we're comfortable taking on ourselves, so I'm going to bring in an electrician. I really appreciate the help though!
Old 05-13-2013, 01:40 PM   #15
Licensed Pro
Excellent decision!
How to replace your clothes line Fantastic Remodeling 5 08-17-2013 09:17 AM
Armored cable shell as conduit? sixspeed Electrical 13 10-18-2012 03:45 PM
Main water line, meter to house ckc Plumbing 15 09-28-2012 09:15 PM
Checking Cable line joedadog Home Theater 12 02-22-2007 12:13 AM