Old 07-18-2008, 09:21 AM   #1
Hardwired Smoke detector wiring
Most jurisdictions require 14/2 from a 15A circuit to the first detector then 14/3 to each one in the chain beyond. While they need far less current than this circuit would provide, I was told the practical reason for this was the difficulty of finding 5 amp breakers to protect lighter wire- and also if you take the feed from a lighting circuit the wire size must match. Sounds reasonable to me.
What would make more sense (since I dont believe the Smoke detectors use the gound) is to allow 14/2 wire (w/ ground)to interconnect them using the ground wire for the 5V /low current signal leg. (Perhaps taping this bare wire red or yellow). Does anyone know if this would meet code?
BTW- Biloxi MS requires 12/3 for the smoke circuit! Go figure.
whisper is offline   Reply With Quote
Old 07-18-2008, 09:41 AM   #2
Electrical Contractor
Using the bare ground wire for anything other than the ground is not legal.
Do it the proper way and run the 3 cable between the smokes.
You are not the only one that is required to use #12 wire. I can't use #14 for anything!
Yes I am a Pirate, 200 years too late. "Jimmy Buffett"
Old 07-19-2008, 06:46 AM   #3
Master Electrician
JohnJ0906's Avatar
That ground is the fault path if there are any problems with that circuit. Just because a smoke detector doesn't connect to it doesn't mean it isn't necessary.
John from Baltimore
One Day at a Time
"Experience is what you get when you were expecting something else"
"The bitterness of low quality lingers long after the sweetness of low cost is forgotten"
JohnJ0906 is offline   Reply With Quote
Smoke Detector, Intermittent Chirping Rod Electrical 18 02-23-2008 07:46 PM
Masons: Smoke Shelf removal? BarryKaraoke HVAC 4 01-12-2008 07:31 PM
Hardwired Smoke Detector question NateHanson Electrical 18 11-10-2007 09:10 PM
GFCI and Smoke alarm circuit issues 00u6166 Electrical 9 10-30-2007 03:41 PM
12 Smoke Alarms sootybuttercup Electrical 8 09-19-2006 09:06 PM