Old 01-17-2009, 10:57 AM   #1
DIY'er
jamiedolan's Avatar
Grounding Wire Size
HI;
I just want to verify that I understand this correctly. Grounding rods never require a larger wire size then 6 AWG, even if the service is 200A. However my understanding in that the bonding wire going to the water pipie and gas pipe must be sized to 4AWG for 200 Amp service.
Is this correct?
Jamie
Jamie Dolan - Neenah, WI
Need Help Uploading Photos?
jamiedolan is offline   Reply With Quote
Old 01-17-2009, 11:09 AM   #2
Electrical Contractor
wirenut1110's Avatar
Send a message via AIM to wirenut1110
Grounding Wire Size
For copper, yes.
wirenut1110 is offline   Reply With Quote
Old 01-17-2009, 11:23 AM   #3
DIY'er
jamiedolan's Avatar
Grounding Wire Size
Originally Posted by wirenut1110 View Post
For copper, yes.
Thanks. I always forget to mention that because I always use copper.
Thanks again
Jamie
Old 01-17-2009, 11:26 AM   #4
Electrician
ctsmiths's Avatar
Grounding Wire Size
The grounding electrode conductor is sized according to the Largest Ungrounded Service-Entrance Conductor per table 250.66 ( in the 2002 code book, I didnt have the 2005 with me) but #8 copper and #6 aluminum is the smallest you can use. But if you had over sized wires feeding your panel, you would need to size the gounding conductor larger also. Ex: If you feed your panel with a #1/0 AWG you would use a #6 ground , but if you had to size up due to voltage drop or some other reason to #2/0 AWG you would need a #4 AWG for the ground. So you'll need to verify the feeders before you consider the ground size. hope this helps
ctsmiths is offline   Reply With Quote
Old 01-17-2009, 11:29 AM   #5
Electrician
Grounding Wire Size
Check out 250.66 (A)
chris75 is offline   Reply With Quote
Old 01-17-2009, 11:34 AM   #6
Grounding Wire Size
Jamie, if you're not using over 3/0 cu then the #4 is fine.
Old 01-17-2009, 11:34 AM   #7
DIY'er
jamiedolan's Avatar
Grounding Wire Size
Originally Posted by chris75 View Post
Your talking about an equipment ground, not a GEC. check out 250.66 (A)
The grounding rods connection the SE is always 6awg correct?
And on 200A service the bond to the other metal in the home would be 4awg or smaller awg (i.e. 2awg 0awg).
All copper.
That's correct isn't it?
Jamie
Old 01-17-2009, 11:37 AM   #8
DIY'er
jamiedolan's Avatar
Grounding Wire Size
I think the SE cable is 3/0 AL. We are not planing to replace that at this point. If the SE cable was larger than 3/0 would I need to make the bonding connection to the water pipe with a larger size wire thatn 4 awg copper?
Jamie
Old 01-17-2009, 11:37 AM   #9
Electrician
Grounding Wire Size
Originally Posted by jamiedolan View Post
HI;
As long as the ground rod is the only connection for that GEC.
Old 01-17-2009, 11:44 AM   #10
Electrician
Grounding Wire Size
You can have a 2000 amp service, and if you choose to run a seperate GEC to groundrods then #6 is all that is required.
All copper.
Jamie
Bonding the water and any other required Grounding Electrodes would be off of Table 250.66.
Old 01-17-2009, 11:53 AM   #11
Grounding Wire Size
When I said "if you're not using over 3/0" earlier it's because you said you always use copper. For 200 amps you need 4/0 aluminum. The range for aluminum is 4/0-250 for a #4.
Wire size for dryer jamiedolan Electrical 14 01-15-2009 06:43 AM