Grounding Wire - Electrical - DIY Chatroom Home Improvement Forum
Old 01-12-2012, 09:45 PM   #1
grounding wire
does anyone know if you can use thhn/thwn for a grounding wire buried directly in the earth? i am going toruneither 1/0 al or 2 xlpe cu and need to rund a grounding wire...i heard you could even use a bare for the grounding wire...any input will be appreciated...thanks
marty56 is offline   Reply With Quote
Old 01-12-2012, 10:20 PM   #2
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
Whatever you use must have direct burial written on the outside jacket of insulation.
No you cannot use Thhn/Thwn ... Thwn is wet rated for using inside buried conduit but it is not rated for direct burial.
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 01-12-2012, 10:27 PM   #3
thanks....someone at an electrical supply said you could use thhn for the grounding wire or even a bare wire....buried directly...didnt think that was right...but didnt know...
Old 01-13-2012, 01:26 PM   #4
Rewards Points: 204
Are you asking about the EGC (equipment grounding conductor) or the GEC (grounding electrode conductor)?
Old 01-13-2012, 02:18 PM   #5
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,974
I was wondering the same thing.
I hope they (the NEC) clarify the whole bonding/grounding thing soon. When a DIY says "the ground wire" no one knows what they are talking about until they explain it.
The Following User Says Thank You to Speedy Petey For This Useful Post:
J. V. (01-14-2012)
Old 01-13-2012, 02:40 PM   #6
Licensed electrician
Rewards Points: 1,794
If the OP is asking about a GEC, it seems contradictory that a bare conductor be allowed, but an insulated one would need to be listed for direct burial.
Old 01-13-2012, 08:58 PM   #7
grounding wire
i am running 1/0 al 150 feet.. (total..breaker to beraker)..100 amp service...direct burial ...its triplex and need to run a grounding wire with it and float the neutral at the subpanel...was told at a electrcial supply house you could run bare copper or thwn...i think im gonna try to find #4 use ... for the grounding wire and be done with it...
Old 01-14-2012, 03:02 AM   #8
Semi-Pro Electro-Geek
Rewards Points: 2,970
I would argue that it's a bare conductor sleeved in plastic.
mpoulton is offline   Reply With Quote
Old 01-14-2012, 05:24 AM   #9
Rewards Points: 3,256
Do the wire manufactures not make a direct burial 4 conductor cable that will fit your needs? The equipment grounding conductor (EGC) is a very important conductor (more important than the hots IMO) and I would want that protected as well as the other conductors. I'm not sure you can even run the EGC outside of the cable assembly.
zappa is offline   Reply With Quote
Old 01-14-2012, 11:18 AM   #10
i called several places....quad plex they dont have....need to call a few more places i guess....rather use that...but if not...ill run triplex 1/0 al with a #4 al use...grounding wire with it....thanks
Tags
grounding wire
my Firex hard wire smoke alarms have no grounding amakarevic Electrical 11 01-14-2012 08:25 AM
convert 3 wire range junction box to receptacle filby Electrical 0 06-05-2011 01:33 AM
Main grounding electrode wire to panel rovers1973 Electrical 4 03-18-2010 06:18 PM
romex with thin grounding wire dogbone Electrical 16 01-10-2009 08:40 PM
Grounding conduit instead of using a ground wire? stringtheories Electrical 10 08-02-2008 12:42 PM