Grounding Using Plastic Boxes? - Electrical - DIY Chatroom Home Improvement Forum
Old 01-04-2009, 06:44 PM   #1
DIY Expert in Training!
Grounding using plastic boxes?
I am rewiring my gutted garage using the blue recepticle boxes. These do not have the ground like metal boxes. How do I ground the circuit?
Thanks!
gone_fishing is offline   Reply With Quote
Old 01-04-2009, 06:51 PM   #2
Rewards Points: 2,350
Thanks!
With the bare ground wire inside the cable.
Old 01-04-2009, 06:53 PM   #3
So, just keep twisting the grounds together along the circuit?
Old 01-04-2009, 07:05 PM   #4
joed's Avatar
Rewards Points: 12,002
Yes and connect to the receptacles and switches. No connection to the box when plastic.
Old 01-04-2009, 07:06 PM   #5
Rewards Points: 150
The bare ground wire connects to any conductive material, like the metal yokes on the recepticals and switches with the green ground screw and runs back to the ground bar in the service panel and then, most likely to grounding rod(s). This is to protect any parts of equipment from becoming energized in the event of a short.
As the blue boxes are plastic, there is no need to ground them. Should you use any metal boxes, include them in the equipment grounding path with a pigtail to a ground screw within the box.
I'm gonna hurl myself against the wall
because I'd rather feel bad than not feel anything at all
Warren Zevon
handifoot is offline   Reply With Quote
Old 01-04-2009, 07:13 PM   #6
Electrical Contractor
kbsparky's Avatar
To an extent, yes. But you still have to use a listed, pressure-type connector, such as a wire-nut, or crimp sleeve to be Code compliant.
And be sure to use a pigtail from those grounding crimps or wire-nuts to any green terminal on your switches or receptacles.
Old 01-04-2009, 08:08 PM   #7
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
The effective ground fault path has nothing to do with ground rods or any other earthing electrode. The bonding of metal parts in a branch circuit to the EGFP is to clear ground faults and shorts as the fault current seeks its source. Ground rods are for lightning and other high voltage events.
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 01-04-2009, 08:40 PM   #8
Rewards Points: 150
Sorry stubbie, you are the pro here.Just that it gets a little confusing to me as the bare ground wires and the white neutral wires are connected to bars that are bonded together which in turn are connected to the ground rods.
Warren Zevon
Old 01-04-2009, 09:00 PM   #9
UAW SKILLED TRADES
Stubbie's Avatar
No problem handifoot. My point was only to clarify. System neutral current and fault current seeks the source.... the transformer center tap. It does not flow to the ground or earth via the grounding electode system. The neutrals and grounds are bonded at the neutral bar so that the current can utilize the service neutral to return to the source. I made a diagram to try and illustrate this.....
Stubbie
Old 01-05-2009, 12:36 AM   #10
Rewards Points: 150
Thanks Stubbie, I really appreciate the time you take to educate folks like me
Warren Zevon
Blue plastic receptical/switch boxes used as junction boxes? alexz Electrical 7 04-09-2013 09:40 PM
wiring outlet boxes, steel or plastic? DangerMouse Electrical 17 07-20-2008 01:05 PM
Anyone want to take a shot at why #6 to attach antenna ground to breaker? Piedmont Electrical 44 01-08-2008 05:11 PM
plastic or metal boxes for outlet wiring? yummy mummy Building & Construction 9 12-31-2006 02:37 PM
Plastic "Old Work" wall box - Grounding Screws? strohs19 Electrical 4 01-14-2006 07:46 PM