Grounding A Swimming Pool Bonding Grid - Electrical - DIY Chatroom Home Improvement Forum
Old 05-24-2011, 09:58 PM   #1
Grounding a swimming pool bonding grid
Is there any benefit (or harm) to grounding the bonding grid of an in-ground swimming pool? My pool builder says that most electricians do it, but article 680 is silent.
Thanks,
Sim
Simbilis is offline   Reply With Quote
Old 05-25-2011, 03:01 AM   #2
Semi-Pro Electro-Geek
Rewards Points: 2,938
What do you mean, exactly? I can't imagine a pool bonding grid that isn't already automatically grounded. The bonding grid is just about the best possible grounding electrode imaginable.
mpoulton is offline   Reply With Quote
Old 05-25-2011, 04:04 AM   #3
Sorry. By grounding, I meant connecting the grid to the ground rod for the pool subpanel.
Old 05-25-2011, 05:46 AM   #4
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,956
Most electricians don't know 680 very well, that is the problem. Many electrician are still not clear on the whole grounding/bonding thing in general.
NO, there is NO benefit nor is it required by code to doing this, so WHY do it? the code is so overkill in some areas (680 for example) already. If they don't required it that is saying something.
680.26 Equipotential Bonding.
(A) Performance. The equipotential bonding required by this section shall be installed to reduce voltage gradients in the pool area. See related Staff Note
(B) Bonded Parts. The parts specified in 680.26(B)(1) through (B)(7) shall be bonded together using solid copper conductors, insulated covered, or bare, not smaller than 8 AWG or with rigid metal conduit of brass or other identified corrosion-resistant metal. Connections to bonded parts shall be made in accordance with 250.8. An 8 AWG or larger solid copper bonding conductor provided to reduce voltage gradients in the pool area shall not be required to be extended or attached to remote panelboards, service equipment, or electrodes.
The Following User Says Thank You to Speedy Petey For This Useful Post:
Simbilis (05-25-2011)
Old 05-25-2011, 05:52 AM   #5
Lic Elect/Inspector/CPO
This is a true about some electricians and on top of that each area may have it own requirements.
NJMarine is offline   Reply With Quote
Old 05-25-2011, 06:21 AM   #6
Originally Posted by NJMarine View Post
.......and on top of that each area may have it own requirements.
Have you ever known or heard of any place that requires an EBG be connected to an electrode?
Old 05-25-2011, 06:40 AM   #7
NO
My point was that areas can decide not to enforce certain parts of the NEC.
Ground rod is one of these, I have not been required to install one.
Old 05-25-2011, 08:04 AM   #8
Registered User
Termite's Avatar
Pool bonding is all about equipotential between all metal parts in and around the pool, not grounding a fault. Attaching the grid to the panel or installing a ground rod has no benefit, is not required in the code, and should not be required. Electricians that do so demonstrate very little understanding of the actual purpose of the bonding grid IMHO.
Old 05-25-2011, 11:46 AM   #9
There is essentially no reason to connect the bonding grid to a ground rod, especially since the bonding grid is a better grounding electrode than any rod could ever be. However, it's worth noting that any properly installed bonding grid is already connected to the system's grounding electrodes. The bonding grid includes connections to the pump motor frame and light niche, both of which are grounded and bonded to the panel and thus connected to the system grounding electrodes.
Swimming pool equipment bonding Boursalians Electrical 7 05-10-2011 01:31 PM
Tips on how I can get this electrical job done for a hot tub in backyard. the punisher Electrical 34 08-24-2010 06:08 PM
Pool bonding grid Our4boys Electrical 12 08-07-2010 01:39 AM
Pool Care Guide scottiedog Landscaping & Lawn Care 16 06-07-2008 08:41 PM
Wire size for 300watt trans, 3 way 100ft Al the Diy guy Electrical 16 03-22-2008 08:46 PM