Old 08-18-2011, 08:14 PM   #1
Grounding sub-panel at pool house
My read of the NEC is that sub-panels should never have the neutral and ground bonded together. I also understand that separate structures require their own grounding rod. So, here's my issue:
We have a pool-house roughly 100' from the main house. I have already run 1.5" grey PVC electrical conduit in a 125' trench containing four 6 gauge conductors with the intent of setting up a sub-panel. I believe based on the wire gauge and temperature ratings, I can use a 60 or 65A 2P breaker for this run to a main-lug sub-panel with separate grounding and neutral terminal strips. The issue I don't understand is do I really need to use a grounding rod at the pool house? If so, do I connect it into the grounding bar of the sub-panel? Do I still need to bring ground in from the main panel's grounding bar, or do I not need to use the 6 ga ground wire I have in the conduit? My sense is that even with a separate ground rod at the pool house, it would be best to connect the two grounding rods together with that 6 ga wire. I really don't understand the purpose of having a separate grounding rod at the pool house.
Thanks for any and all info.
CraigMW is offline   Reply With Quote
Old 08-18-2011, 08:18 PM   #2
Lic Electrical Inspector
electures's Avatar
Detached structure requires a ground rod. #6 neutral has to be white entire length. 60a on #6 unless all terminations are 75C. Ground rod connects to the ground bar at subpanel along with ground wire from main panel.
All responses based on the 2011 NEC.
If you live in New Jersey click
. All other states click
Please check with local, county and state officials as laws may vary.
Sizing motors
. Online motor calculator
. Online calculators
electures is offline   Reply With Quote
The Following User Says Thank You to electures For This Useful Post:
CraigMW (08-18-2011)
Old 08-18-2011, 08:22 PM   #3
Wow, that was quick! Thanks for the info.
Old 08-18-2011, 08:24 PM   #4
electures's Avatar
Welcome!
Sizing motors
Old 08-18-2011, 08:25 PM   #5
BTW, regarding "60a on #6 unless all terminations are 75C";
Does this mean that if terminators are 75C or above, that I can go with higher ampacity breaker?
Also, the four wires in the conduit are red and black (for each side of 220V), white (neutral) and green (ground).
Old 08-18-2011, 08:29 PM   #6
electures's Avatar
If all terminals are 75C then the higher ampacity can be used. Colors are good also.
Sizing motors
Old 08-18-2011, 08:53 PM   #7
Master Electrician
Seperate structure requires a min disconnect.
brric is online now   Reply With Quote
Old 08-18-2011, 09:31 PM   #8
electures's Avatar
What about six motions of the hand?
Sizing motors
Old 08-18-2011, 09:55 PM   #9
Licensed electrician
Doin the hand jive?
Old 08-18-2011, 10:03 PM   #10
electures's Avatar
Originally Posted by Jim Port
Doin the hand jive?
Baby. Lol
Sizing motors
Old 08-19-2011, 01:22 AM   #11
I'm not sure if I follow. Do you mean that the sub-panel requires a main breaker and not main lug? Or alternatively, that the lines coming into the sub-panel require a switch? I thought the breaker in the main panel would cover this?
Old 08-19-2011, 08:19 AM   #12
Master Electrician
You need to be able to shut off all power to the structure with 6 or fewer motions of the hand. If your panel will have more than 6 circuits then the panel needs a main breaker.
Old 08-19-2011, 11:08 AM   #13
Okay, that makes sense.
bonding and grounding of pool pump/motor gpike19 Electrical 2 07-22-2011 01:18 PM
Splitting your input before your house panel? Jim Johnstone Electrical 22 04-09-2011 12:23 PM
Weird wiring in house fdmillion Electrical 7 02-26-2010 01:57 AM
Garage Wiring issues jimmyfloyd Electrical 20 06-08-2009 03:57 PM
sub panel grounding jprince Electrical 2 05-04-2009 07:15 PM