-   -   Grounding sub-panel at pool house (http://www.diychatroom.com/f18/grounding-sub-panel-pool-house-114543/)
CraigMW 08-18-2011 07:14 PM
My read of the NEC is that sub-panels should never have the neutral and ground bonded together. I also understand that separate structures require their own grounding rod. So, here's my issue:
We have a pool-house roughly 100' from the main house. I have already run 1.5" grey PVC electrical conduit in a 125' trench containing four 6 gauge conductors with the intent of setting up a sub-panel. I believe based on the wire gauge and temperature ratings, I can use a 60 or 65A 2P breaker for this run to a main-lug sub-panel with separate grounding and neutral terminal strips. The issue I don't understand is do I really need to use a grounding rod at the pool house? If so, do I connect it into the grounding bar of the sub-panel? Do I still need to bring ground in from the main panel's grounding bar, or do I not need to use the 6 ga ground wire I have in the conduit? My sense is that even with a separate ground rod at the pool house, it would be best to connect the two grounding rods together with that 6 ga wire. I really don't understand the purpose of having a separate grounding rod at the pool house.
Thanks for any and all info.
electures 08-18-2011 07:18 PM
Detached structure requires a ground rod. #6 neutral has to be white entire length. 60a on #6 unless all terminations are 75C. Ground rod connects to the ground bar at subpanel along with ground wire from main panel.
CraigMW 08-18-2011 07:22 PM
Wow, that was quick! Thanks for the info.
electures 08-18-2011 07:24 PM
Welcome!
CraigMW 08-18-2011 07:25 PM
BTW, regarding "60a on #6 unless all terminations are 75C";
Does this mean that if terminators are 75C or above, that I can go with higher ampacity breaker?
Also, the four wires in the conduit are red and black (for each side of 220V), white (neutral) and green (ground).
electures 08-18-2011 07:29 PM
If all terminals are 75C then the higher ampacity can be used. Colors are good also.
brric 08-18-2011 07:53 PM
Seperate structure requires a min disconnect.
electures 08-18-2011 08:31 PM
What about six motions of the hand?
Jim Port 08-18-2011 08:55 PM
Doin the hand jive?
electures 08-18-2011 09:03 PM
Originally Posted by Jim Port
Doin the hand jive?
Baby. Lol
CraigMW 08-19-2011 12:22 AM
I'm not sure if I follow. Do you mean that the sub-panel requires a main breaker and not main lug? Or alternatively, that the lines coming into the sub-panel require a switch? I thought the breaker in the main panel would cover this?
brric 08-19-2011 07:19 AM
You need to be able to shut off all power to the structure with 6 or fewer motions of the hand. If your panel will have more than 6 circuits then the panel needs a main breaker.
CraigMW 08-19-2011 10:08 AM
Okay, that makes sense.