Grounding Service Panel - Electrical - DIY Chatroom Home Improvement Forum
Old 01-25-2011, 04:29 PM   #1
grounding service panel
If a house is grounded outside via a grounding rod into the earth, does it also have to be grounded to a water pipe in the basement?
klaus135 is offline   Reply With Quote
Old 01-25-2011, 04:40 PM   #2
joed's Avatar
Rewards Points: 12,872
It's not actually grounded to the water pipe. The proper term is the water pipe is bonded to the panel ground. The purpose being to cause the breaker to trip if power somehow gets applied to the pipes.
Yes it needs to be done even with ground rods present.
Old 01-25-2011, 04:45 PM   #3
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,956
Well, if the water pipe entering the house is metallic and in contact with the the earth for 10' or more it should be used as an electrode. There are certain requirements in this case, and it also serves the purpose of bonding.
Speedy Petey is online now   Reply With Quote
Old 01-25-2011, 04:56 PM   #4
Master Electrician
Rewards Points: 3,870
I believe it to be a grounding electrode, not just a bond, as Speedy has said.
brric is online now   Reply With Quote
Old 01-25-2011, 07:00 PM   #5
joed's Avatar
If there are ground rod(s) present as the OP asked is the pipe still considered an electrode?
Old 01-25-2011, 07:42 PM   #6
Rewards Points: 1,512
If the plumbing is capable of providing a grounding electrode (metal cold water pipe extends out from the foundation the 10 feet) you might as well use that as the (primary) grounding electrode. Seeing that you have to bond it to the electrical system ground.
Gas piping must also be bonded to your #6 ground wire network (grounding electrode system) but the gas pipe exiting the house does not count as a grounding electrode. For gas piping, the National Electric Code allows the ground wire that serves a hard wired electrical appliance that uses gas to be the bond, going back to the panel via the respective branch circuit although some cities require a #6 wire direct to the grounding eletrode system.
Idiosyncrasy: For services of more than 100 amps, you need #4 wire between the panel and the water pipe as a ground electrode but #6 will still suffice going to ground rods.
Old 01-25-2011, 08:24 PM   #7
Master Electrician
Absolutely. For other than lightning ground rods are pretty much useless as a grounding means.
Old 01-25-2011, 08:47 PM   #8
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
Originally Posted by Speedy Petey View Post
Well, if the water pipe entering the house is metallic and in contact with the the earth for 10' or more it must be used as an electrode. There are certain requirements in this case, and it also serves the purpose of bonding.
Petey...I know you know better.
and a water pipe with the 10 feet contact yada yada is always considered a grounding electrode. In fact, it is the first in the the list of electrodes in the NEC.
Old 01-25-2011, 08:58 PM   #9
Nap, I'm not sure what you mean.
Although I didn't mean to imply that he had to do this after the fact. But it should have been done when the service was installed.
Old 01-25-2011, 09:03 PM   #10
nap
You talking to me?
nap's Avatar
you had typed "should" be used. I corrected it to "must" be used.
Old 01-25-2011, 09:15 PM   #11
Master Electrician
Nap, why do so many people not understand this?
Old 01-25-2011, 09:24 PM   #12
nap
You talking to me?
nap's Avatar
well, most electricians do, at least the ones that I know. They should know anyway. When it comes to laymen, all bets are off.
Maybe it's because a lot of homes currently use plastic pipe for the water supply so it isn't as common as it once was.
Old 01-25-2011, 09:34 PM   #13
I see, yeah, I wrote that wrong.
Wiring Size Calculations for New Service CorinthWest Electrical 7 12-07-2010 11:36 AM
200 amp panel w/100 amp service PirateKatz Electrical 8 12-26-2009 03:42 PM
Upgrade Service Panel - Do I need a new meter? El Kati Electrical 6 08-11-2008 07:35 PM
Nuetral from feeder cable to main panel question? TW Lucas Electrical 14 05-08-2008 11:33 AM
New service panel + Generator transfer Nhrafan Electrical 1 04-21-2008 11:05 PM