Grounding pigtails
Had a thought while reading another post...
Why is it that when you use NM cable with metal boxes, you need to pigtail the grounds to the box and to the device... but when using conduit, the device does not need to be grounded to the box other than via the screws?
If the screws on the device are good enough to make the ground connection in a conduit setup, why are they not sufficient in an NM setup?
SquishyBall is offline   Reply With Quote
Old 04-16-2013, 09:02 AM   #2
Rewards Points: 349
Conduit is considered the ground path (unbroken metal clear from box to panel). With NM, that metallic path is not there, so it uses the ground wire as the path.
al_smelter is offline   Reply With Quote
Old 04-16-2013, 09:14 AM   #3
Licensed electrician
Rewards Points: 1,876
From 2011 NEC 406.4(C) Methods of Grounding.
The equipment grounding conductor
contacts of receptacles and cord connectors shall be
grounded by connection to the equipment grounding conductor
of the circuit supplying the receptacle or cord connector.
Old 04-16-2013, 11:13 AM   #4
Rewards Points: 150
Of course. But that's not the question.
So with NM, and say two wires in and out. ground 1 and ground 2 are joined with two pigtails - one to the metal box and one to the device.
With conduit, the metal raceway is the ground, fine. Yet you do not need to ground your device. The connection via the screws is sufficient.
Why is that screws connection not sufficient with NM with a grounded metal box?
contacts of receptacles and cord connectors shall be grounded by connection to the equipment grounding conductor
But with conduit it's ok to just use the screws for that. Why are the screws less effective w NM in a metal box. The metal box is just as grounded (from the pigtail) as it is w conduit (from the metal raceway).
Old 04-16-2013, 11:54 AM   #5
Semi-Pro Electro-Geek
Rewards Points: 2,990
I don't get it either, and have often wondered about this. It seems to me that a grounding connection should only be required in one location at each box. Bond the box, and the devices should be effectively bonded too. Bond a device, and the box should be effectively bonded too (and probably any other devices in that box). Pigtailing everything seems totally redundant. I would understand it if the device-to-box connection were never considered acceptable for bonding. But it is allowed if the box is grounded through conduit, so the box-to-device connection has been tested and found adequate under those circumstances. Why is that a special case? Why isn't that connection always considered good enough? I don't ever expect answers to these questions. The NFPA often seems like a phony psychic, handing out dubious advice with no explanation.
I am a lawyer, but not your lawyer. And who cares anyways? We're here to talk construction. This is DIY advice, not legal advice.
mpoulton is offline   Reply With Quote
The Following User Says Thank You to mpoulton For This Useful Post:
junkcollector (04-18-2013)
Old 04-18-2013, 09:38 AM   #6
Dana56's Avatar
Always pigtail grounds to box and device no matter what it dont take much and its good practice. Dont think anybody relies on conduit as ground anymore, u always pull a ground in pipe
Dana56 is offline   Reply With Quote
Old 04-18-2013, 04:17 PM   #7
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
What makes you think you have to?
Old 04-18-2013, 04:22 PM   #8
E2 Electrician
Thats a nice opinion you have....but not required.
Old 04-18-2013, 04:26 PM   #9
E2 Electrician
And in some cases that's all you are required.
This is true if you are using self grounding receptacles, switches are allowed to be bonded with the 6-32 alone....
You cannot have the device solely bond the box, think about it, what if the device is removed?
Old 04-18-2013, 04:33 PM   #10
E2 Electrician
I know the pictures show EMT as the wiring method, but any wiring method can be applied to this.
Old 04-18-2013, 05:30 PM   #11
That is a good point. I suppose the code writers are concerned that someone would remove the device that is bonding the box, and replace it incorrectly.
Old 04-18-2013, 08:02 PM   #12
Note that only applies to surface mounted boxes and certain covers. Flush mount needs both to be bonded together.
k_buz (04-18-2013)
Old 04-18-2013, 09:03 PM   #13
Dana56's Avatar
Glad u like it... Like to go a little more than "minimum requirement" never know if set screws are properly tightened to ensure good ground thanks for input
Old 04-18-2013, 09:35 PM   #14
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
This is true, however, they do make listed self-grounding receptacles that would not need a ground run to it.
The Following User Says Thank You to k_buz For This Useful Post:
stickboy1375 (04-19-2013)
Old 04-18-2013, 10:19 PM   #15
Dana56's Avatar
Bonding bushings or locknuts mite be required too if the box has concentric knockouts just another nice opinion )
2-2-4 SEU - Smaller Neutral? BRT Electrical 18 09-23-2012 09:25 PM
Replacing Light Fixture with No Ground Wire in Home panorama Electrical 42 09-14-2012 09:35 AM
Bare grounding pigtails? smata67 Electrical 2 05-27-2012 07:27 AM
Need to know if my grounds and neutrals are connected right dorlow Electrical 185 01-15-2012 02:54 PM
NEC Question Jafsvcs Electrical 1 06-13-2007 05:45 PM