Old 08-10-2006, 02:39 PM   #1
Grounding new service
I have been reading alot about grounds and bonding in a new 200 amp panel and would like to try and get some clarification.
when switching over from a 100 amp panel with the ground from the service coldwater pipe to the neutral bussbar.
The new 200 amp panel has 2 bussbars one which will accomodate the incoming neutral wire ( this bussbar should be grounded) , the second bussbar also has a large solderless connector and an attached metal strip with a copper nub and green screw. Does this bussbar need to be grounded and how....
Would 2 cu rods have to be driven in the soil for grounding and could the coldpipe connection still be used ( of course changing the wire size to at least #6)
The SE is cable no conduit.
any info please.
TonyD
TonyD is offline   Reply With Quote
Old 08-10-2006, 05:34 PM   #2
Licensed Electrical Cont.
Speedy Petey's Avatar
Ok, first off, if you have copper or metal water pipe coming into the house you MUST use it as the primary grounding electrode. This means you have to connect to it within 5' of where it enters the house and jump around any meters and plastic filters, etc.
You must still supplement this with a ground rod or other electrode. Rods are most common. There is a minimum resistance rule to be met and testing is not easy so most simply install two rods (6' apart minimum).
The wire to the rods only can be #6. The wire to the water pipe must be #4.
I'm really not clear on your description of the bars in the new panel, but this is irrelevant. ALL neutral and ground bars get bonded to the panel box. Neither bar remains isolated. So if there is a bond strap/screw, use it.
Old 08-11-2006, 07:46 AM   #3
Thanks Speedy,
My water service entrance into the house is copper and approximately 3-4' from the panel. The bussbars Im talking about are one is for the neutral's and the other the ground...
So I will run the #4 Cu from the cold water pipe to which bussbar
The #6 wire from the groundig rods , should the wire be ran in conduit or just ran into the basement straight to the panel. This wire connects to the same neutral bussbar or the other one. Im sorry to be redundant but this is how I learn, That second bussbar is the one that has the bonding strap.
TonyD
Old 08-11-2006, 11:25 AM   #4
Either.
With #6 no conduit is necessary. Just keep it clear of immediate damage when outside. Make it as short as possible to the rods.
Again, either bar.
Old 08-11-2006, 01:23 PM   #5
Speedy, thanks for the input......I appreciate it...
Whats your view on alum vs Cu for service. Just curious.
Tony D
Old 08-11-2006, 02:01 PM   #6
We use AL almost exclusively. I cannot even get SE cable in CU around here.
Installed properly AL is perfectly fine and just as safe as CU.
Old 08-11-2006, 03:22 PM   #7
Electrical contractor
RobertWilber's Avatar
I think that you will find, if you look closely, that the two neutral bars are connected by a bar that runs behind the busbar insulation sheet.
They are installed like this by certain manufacturers to facilitate connection of the neutral and ground conductors in a cable near the point where the "hot" is attached to the breaker.
The one with the "big lug" is so that you can terminate the 4/0 or 2/0 aluminum SE neutral as a single conductor.
And remember that you only need #6 to the ground rod. One rod is enough here, but I have been reading about a lot of places where the AHJ "authority having jurisdiction" requires 2 rods, so you had best check
RobertWilber is offline   Reply With Quote
Old 08-11-2006, 11:18 PM   #8
Ok guys thanks for the info it was really helpfull
  1. On another note is it rule of thumb that a light bar over the bathroom vanity be 60" to center from the floor.
  2. Also what is the height of an outlet next to a vanity.
Thanks Again
TonyD
Old 08-11-2006, 11:33 PM   #9
1- IMO 60" is too low. Consider your mirror first and then figure fixture height. 66"-72" is a better range.
2- I do bath vanity receptacles at 44" to the top of the box. This keeps it closer to the counter top so cords are not hanging as high, and makes sure there is no conflict with a chair rail or wainscotting which is typically at 48".
Old 08-12-2006, 09:52 PM   #10
Great, Thanks again for the help.
TonyD
Old 08-21-2006, 11:38 AM   #11
Speedy,
Should the the # 4 and #6 wires be bare....
TonyD
Old 08-21-2006, 12:03 PM   #12
Bare solid wire is probably cheeper, but the code does not say if you need to use solid or stranded, bare or covered for Grounding Electrode Conductors.
Take your pick. Unless there is a local code that we would not be aware of.
jwhite is offline   Reply With Quote
200 amp panel with a 100 amp service? alexz Electrical 10 07-29-2007 11:00 PM
upgrading service cable Clutchcargo Electrical 1 06-22-2007 11:04 AM
NEC Question Jafsvcs Electrical 1 06-13-2007 06:45 PM
Service upgrade rondo Electrical 1 05-21-2007 07:19 PM
Suspected open/loose service neutral mrtomwj Electrical 5 09-28-2006 09:46 AM