Grounding Metal Boxes and Outlets - Confused by Something Simple
Long time lurker, first time poster. I have flogged the search engines for an answer to what I thought was a simple question and come up with too many confusing answers. Here is my question -
I am installing multiple outlets on a circuit. Using brand new 12-2 romex to rewire outlets. My circuit is properly grounded (updated box at main panel with rod and brand new interior box with ground bar). In the past, I have always used plastic boxes, but in this situation, I am having to use metal boxes. When using metal boxes for duplex outlets, are you required to ground to the metal box FIRST before the outlet itself? I have been told that if you ground to the outlet (the outlet ground screw), the entire thing is grounded when you screw the outlet into the metal box. Makes sense, but that's not the way I was taught to do it. I was taught this way: (1) Insert incoming (powered from circuit) wire. Attach its ground wire to the metal box via ground screw AND attach it to the outlet ground. (2) Insert outgoing (to next outlet) wire and attach its ground wire to the metal box. (3) Repeat until you get to the last outlet. (4) Last outlet on circuit - attach ground wire to box AND outlet. Who is correct? Thanks. |
Help, please!
I always twist the incoming and outgoing wires together,then pigtail from there to the box and outlet.
Everyone seems to have their own method. On new work I leave the cable that feeds the power to the box extra long. I then twist all of the grounds and lock it all together with a a green wire nut leaving the long one to come through the hole in the wire nut. I wrap the ground screw to bond the box and trim what's left to the correct length, wrapping the end around the green ground lug of the device.
Thanks so much for your help. Because neither one of you picked the method someone else told me is acceptable, I am doing it the way I learned how, as it is the closest to what you do and equally safe.
The answer is none of the above.
You ground the metal box and the receptacle in each box. Not just at the first one in the circuit. Like already said. make up all the grounds, neutrals and hots with pigtails for the receptacles. This is when you install the grounding jumper. I know it's overkill, but it is the right way to do this. :thumbsup: |
When using metal boxes with receptacles the grounding conductor must attach to the box... now we have some options on having to install a grounding jumper from the box to the receptacle or not... 250.146 (A) Surface Mounted Box. Where the box is mounted on the surface, direct metal to metal contact between the device yoke and the box or a contact yoke or a self grounding receptacle shall be permitted to ground the receptacle to the box. Basic examples (A) type installation... http://i171.photobucket.com/albums/u...75/graphic.jpg http://i171.photobucket.com/albums/u...receptacle.jpg 250.146 (B) Contact Devices or Yokes. Contact devices or yokes designed and listed as self-grounding shall be permitted in conjunction with the supporting screws to establish the grounding circuit between the device yoke and flush type boxes... What that means is, in option (B) if you buy self grounding receptacles, you don't need a bonding jumper from the receptacle to a flush mounted box. In option (A) If using SURFACE mounted boxes, you don't need a bonding jumper if using self grounding receptacles, OR you remove one of the washers on the 6-32 screws on non self grounding receptacles. |
The incoming and outgoing grounds need to be connected to each other and the box, not by using 2 screws into the box.
here ya go. fun reading.
250.148 Continuity and Attachment of Equipment Grounding Conductors to Boxes. Where circuit conductors are spliced within a box, or terminated on equipment within or supported by a box, any equipment grounding conductor( s) associated with those circuit conductors shall be connected within the box or to the box with devices suitable for the use in accordance with 250.148(A) through (E). Exception: The equipment grounding conductor permitted in 250.146(D) shall not be required to be connected to the other equipment grounding conductors or to the box. (A) Connections. Connections and splices shall be made in accordance with 110.14(B) except that insulation shall not be required. (B) Grounding Continuity. The arrangement of grounding connections shall be such that the disconnection or the removal of a receptacle, luminaire, or other device fed from the box does not interfere with or interrupt the grounding continuity. (C) Metal Boxes. A connection shall be made between the one or more equipment grounding conductors and a metal box by means of a grounding screw that shall be used for no other purpose, equipment listed for grounding, or a listed grounding device. (D) Nonmetallic Boxes. One or more equipment grounding conductors brought into a nonmetallic outlet box shall be arranged such that a connection can be made to any fitting or device in that box requiring grounding. (E) Solder. Connections depending solely on solder shall not be used. |
for your added pleasure.
250.146 Connecting Receptacle Grounding Terminal to Box. An equipment bonding jumper shall be used to connect the grounding terminal of a grounding-type receptacle to a grounded box unless grounded as in 250.146(A) through (D). The equipment bonding jumper shall be sized in accordance with Table 250.122 based on the rating of the overcurrent device protecting the circuit conductors. (A) Surface-Mounted Box. Where the box is mounted on the surface, direct metal-to-metal contact between the device yoke and the box or a contact yoke or device that complies with 250.146(B) shall be permitted to ground the receptacle to the box. At least one of the insulating washers shall be removed from receptacles that do not have a contact yoke or device that complies with 250.146(B) to ensure direct metal-to-metal contact. This provision shall not apply to cover-mounted receptacles unless the box and cover combination are listed as providing satisfactory ground continuity between the box and the receptacle. A listed exposed work cover shall be permitted to be the grounding and bonding means when (1) the device is attached to the cover with at least two fasteners that are permanent (such as a rivet) or have a thread locking or screw locking means and (2) when the cover mounting holes are located on a flat non-raised portion of the cover. (B) Contact Devices or Yokes. Contact devices or yokes designed and listed as self-grounding shall be permitted in conjunction with the supporting screws to establish the grounding circuit between the device yoke and flushtype boxes. (C) Floor Boxes. Floor boxes designed for and listed as providing satisfactory ground continuity between the box and the device shall be permitted. (D) Isolated Receptacles. Where installed for the reduction of electrical noise (electromagnetic interference) on the grounding circuit, a receptacle in which the grounding terminal is purposely insulated from the receptacle mounting means shall be permitted. The receptacle grounding terminal shall be connected to an insulated equipment grounding conductor run with the circuit conductors. This equipment grounding conductor shall be permitted to pass through one or more panelboards without a connection to the panelboard grounding terminal bar as permitted in 408.40, Exception, so as to terminate within the same building or structure directly at an equipment grounding conductor terminal of the applicable derived system or service. Where installed in accordance with the provisions of this section, this equipment grounding conductor shall also be permitted to pass through boxes, wireways, or other enclosures without being connected to such enclosures. FPN: Use of an isolated equipment grounding conductor does not relieve the requirement for grounding the raceway system and outlet box. |
Based on the responses, the answer to that question is no, that is not correct and should not be done, which is what I believed. However, now, the latest responses have left me confused again, as it sounds like my method is not correct either. According to the newer responses, I connect the incoming and outgoing to each other and THEN connect to the box and the outlet by pigtail or by leaving the incoming wire longer. Is this correct? |
It doesn't matter if you leave one long or use a pigtail to the box and/or the device. What matters is that the grounds are connected together and to the box and the device.
Got it. Now, reading the code makes more sense too. This site is great. Thanks so much. Now, one day, I learn why (other than the code says so) connecting the two egcs is required rather than connecting both to the box, but I leave that for another day.
| All times are GMT -4. The time now is 12:43 AM. |