Grounding CSST Gas Line - Electrical - DIY Chatroom Home Improvement Forum
Old 09-18-2011, 09:32 AM   #1
Grounding CSST gas line
My metal gas line runs into the house in a finished basement. I can reach where the metal gas line is connected to the CSST. If I clamp the #6 ground wire on the metal pipe just before the CSST connection and run the ground to my bus panel, will that work or MUST the clamp on the metal pipe be on the outside of the house?
rjcaster is offline   Reply With Quote
Old 09-18-2011, 10:10 AM   #2
Rewards Points: 6,652
The NFPA.org website has this info avail, if you want to read through firsthand. As for the bond, when you run back to the panel, in reality you are creating a loop. The bond needs to be tied I do believe to the grounding rod.
The Following User Says Thank You to gregzoll For This Useful Post:
rjcaster (09-18-2011)
Old 09-18-2011, 10:20 AM   #3
Rewards Points: 1,514
The bonding wire from the gas pipe can be connected to (1) the neutral bus in the panel, (2) the ground rod, (3) the main water pipe where it is bonded to the electrical system, or (4) any of the fat ground wires (grounding electrode conductors) connecting the previous three. Whichever is most convenient.
You are bonding the gas piping in your house to the electrical system ground (rod and/or water pipe). The gas pipe itself exiting the house does not qualify as a grounding electrode.
No specific bonding wire is needed for the gas pipes if there is a gas appliance (furnace, etc.) that uses electricity and wired up with a proper ground wire back to the panel.
What is a CSST?
The Following User Says Thank You to AllanJ For This Useful Post:
Old 09-18-2011, 10:46 AM   #4
Allan, I think that they are talking about the plastic sheathed gas piping, that likes to pinhole. Personally I would not touch the stuff, and still like the Black Iron.
Old 09-18-2011, 11:04 AM   #5
Master Electrician
Rewards Points: 3,874
Corrugated stainless steel tubing gas piping must be bonded as per the tubing manufacturer. Either from the iron piping it is connected to or from the brass fitting of the tubing back to the electrical panel. Do NOT attempt to bond the corrugated tubing itself or you will crush it.
brric is offline   Reply With Quote
The Following 2 Users Say Thank You to brric For This Useful Post:
NJMarine (09-18-2011), rjcaster (09-18-2011)
Re-routing main water line (perpendicular to joists) near ductwork and gas line? jjcatal Plumbing 1 03-29-2011 10:18 PM
DIY Comedy--PVC for main water line? Daulton Plumbing 8 03-23-2011 09:03 AM
Can a roof vent identify where my main sewer line exits the house? YerDugliness Plumbing 8 01-26-2010 04:13 PM
grounding electrode conductor question bsperr Electrical 8 12-05-2009 09:23 AM
moving incoming power line and grounding rod amakarevic Electrical 3 07-28-2008 11:24 PM