Old 09-22-2011, 09:53 PM   #1
Grounding at the cabin
I have a cabin with a meter on a pole about 100ft from the road. My cabin is about another 250ft from the pole. The plan is to run 4/0 AL SE cable from the meter to the new cabin. I will then install a 100 amp panel in the cabin. We don't have a utilities, water or gas lines so I think I'm going to have to drive two ground rod, 6 ft apart in a loop from the panel to the 1st rod then the second and back to the panel non stop. The plan is to do the same at the pole with the meter channel attached. I called a expert and I know hes right, I just want to make sure I'm repeating this back correctly. Does this sound right? I've never had to do a service where there are no water or gas lines.
Let me know thanks
scamilleri1228 is offline   Reply With Quote
Old 09-22-2011, 11:59 PM   #2
Average Joe/ex-Navy IC3
gregzoll's Avatar
It is a little overboard. My in-laws sit about a hundred feet from their road, and have a transformer box on their property, due to they are feeding a 5 bedroom cabin, two outbuildings. As for your's, one ground at the meter base, one ground rod at the cabin. As for water, how you you getting that, Well, or just having it trucked in to be placed into a fresh water tank?
: Now listen, Cadet. I've got a job for you. See this button?
: Don't touch it! It's the History Eraser button, you fool!
: So what'll happen?
: That's just it. We don't know. Maybe something bad, maybe something good. I guess we'll never know, 'cause you're going to guard it. You won't touch it, will you?
Old 09-23-2011, 12:16 AM   #3
SE Cable? Nope.
bobelectric is offline   Reply With Quote
Old 09-23-2011, 01:44 AM   #4
Don't know where your from but two ground rods are pretty common in some areas. Otherwise you have to prove 25 ohms or less to poco so ahj. Double check your distance though for some reason eight feet sounds more likely.
AlKapone is offline   Reply With Quote
Old 09-23-2011, 08:12 AM   #5
Licensed electrician
It is a 6' minimum between rods.
How do you plan to support SE cable for 250' from the pole to the cable?
AlKapone (09-23-2011)
Old 09-23-2011, 08:27 AM   #6
Licensed Electrical Cont.
Speedy Petey's Avatar
I think by SE cable he means underground service entrance cable, such as URD.
Six foot separation minimum is code.
WHY 4/0 for a 100A service?????
Where is the POCO's transformer?
Are you aware that you will NOT be able to terminate 4/0 in a 100A panel?
Speedy Petey is online now   Reply With Quote
Old 09-23-2011, 09:14 AM   #7
Code05's Avatar
The Op probably can't, but I can.
Code05 is offline   Reply With Quote
Old 09-23-2011, 10:09 AM   #8
I ment tri-plex or urd, I was going with 4/0 because the meter is 250' in and I'm not sure where the transformer is, I haven't been to the property yet. I will do the calc and post it as soon as I have the numbers. What do you do if the wires won't fit the lugs, I see the photo above but I don't recognize those guys.
Old 09-23-2011, 10:20 AM   #9
Ok, maybe 4/0 a little overboard lol.
CM=2xKxIxD
______
VD
CM=2x21.2x100Ax250ft
______________
5% of 220v
CM=96,363 or 1/0 Al
Old 09-23-2011, 10:49 AM   #10
Code05's Avatar
Use 240v for calc.
Old 09-23-2011, 11:01 AM   #11
I know that silly. That's what I meant.
Old 09-23-2011, 11:04 AM   #12
That's a pretty bold thing to wing off the cuff, 250 feet of cable I mean.
Most any POCO will tell you that 250' is the limit for "standard" size URD cable. Meaning for a 100A SERVICE, you can use #2AL URD.
If the trans is pretty far from the pole then bump it up a size or two, but 4/0 is absurd for this distance.
The Following User Says Thank You to Speedy Petey For This Useful Post:
Code05 (09-23-2011)
Old 09-23-2011, 01:00 PM   #13
Code05's Avatar
Agreed.
Old 09-23-2011, 01:03 PM   #14
Code05's Avatar
I doubt you have a compression tool. T'was a private joke.
As Speedy Petey says, you are oversizing the wire.
Old 09-23-2011, 01:20 PM   #15
gregzoll's Avatar
Derek, why not for the OP, run the drop from the meter to a meter pan, with a blank. Wouldn't that be easier if the drop ever had to be replaced from the remote meter pedestal to the house, instead of pulling directly to the load center in the house?
Grounding sub-panel at pool house CraigMW Electrical 12 08-19-2011 11:08 AM
Grounding rods for tv antennas Wasatch Rebel Electrical 4 06-02-2011 08:23 AM
Grounding from Junction Box too Main tlj Electrical 5 10-25-2009 01:48 AM
BIG PROBLEMS with cabin mud sills and floor scylla2 Building & Construction 1 10-18-2009 09:34 PM