Grounding Bar In Junction Box - Electrical - DIY Chatroom Home Improvement Forum
Old 02-09-2013, 11:27 AM   #1
grounding bar in junction box
There are 4 conduits runs coming from the main panel to a junction box 3 are 3/4 plastic the other is 1 1/4 emt. The rest of the wires coming in from kitchen/ rest of the house to the junction box are romex. 8 circuits of 12/2, 2 circuits 14/2, 1 circuit of 10/3 and 1 circuit of 6/3.
In order to make it look clean and code compliant can you attach all the grounds to a grounding bar then run one ground back to ground bar in the panel ?
The largest ground wire to the grounding bar will be 6 gauge from a stove .What size ground wire will be required from the bar to the panel ?
Thanks for any help
Warchild is offline   Reply With Quote
Old 02-09-2013, 12:00 PM   #2
Electrician
Rewards Points: 150
Yes
Maybe none. Maybe #10 copper.
The ground must be sized to the largest circuit. If the #6 is on, no more than, a 60A breaker then #10 copper ground is correct. Table 250.122.
Glennsparky is offline   Reply With Quote
The Following User Says Thank You to Glennsparky For This Useful Post:
Warchild (02-14-2013)
Old 02-09-2013, 12:42 PM   #3
Electrician
Rewards Points: 150
A code compliant run of EMT, with clean and tight connections and fittings listed for the purpose, is "permitted as an equipment grounding conductor." 358.60.
The #6 stove cable may have a larger egc than #10. that's ok. The cable is generic to fit the most possible applications without retooling.
2-2-4 SEU - Smaller Neutral? BRT Electrical 18 09-23-2012 09:25 PM
Grounding in a plastic receptacle or junction box smcgarry9 Electrical 5 10-20-2011 11:04 AM
grounding old 2 wire junction to grounded junction gm8075 Electrical 3 03-28-2011 11:46 AM
Grounding from Junction Box too Main tlj Electrical 5 10-25-2009 12:48 AM
Anyone want to take a shot at why #6 to attach antenna ground to breaker? Piedmont Electrical 44 01-08-2008 04:11 PM