Grounding 400a Service To 2-200a Panels - Electrical - DIY Chatroom Home Improvement Forum
Old 08-07-2012, 09:36 PM   #1
Grounding 400a service to 2-200a panels
I have a grounding question. I am installing 400a service to my new home. We ran 350MCM wire underground thru 3" conduit from the 2ndary terminal (moped) to the house into a 320A Cooper B-Line meter. From the meter we ran 2 sets of 4/0-4/0-2/0 thru the wall to 2-200a breaker panels ("standard practice", according to my electrical supplier). The ground wire (#4Cu bare) from the grounding rods comes up from the ground and we're curious if there has to be a special splice connecting the ground wire to each breaker panel or can we run thru one breaker panel to then next, say by connecting the ground wire to a ground bus on one panel and running that thru to the next with #4Cu bare or #6Cu in conductor. Different electricians are suggesting different methods and the electrical inspector is unsure, but seems to be leaning towards the "special splice". Any feedback would be appreciated.
Kingb is offline   Reply With Quote
Old 08-08-2012, 05:02 AM   #2
Electrical Contractor
wirenut1110's Avatar
Rewards Points: 510
Send a message via AIM to wirenut1110
You can do it one of 2 ways.
Take a #6 (#4 since you have it already) from one panel through each rod, then do the same for the other panel (use one clamp for each connection unless listed for multiple) or take a #6 through each rod to the first panel and a #4 jumper from panel to panel.
The connection should be made as close as possible to the grounded conductor. Some panels have a lug where the neutral connects to terminate the GEC. If not, I usually terminate on the neutral bar just below where the neutral connects.
Keep in mind, if you think about putting multiple wires under one lug because it fits, make sure that the lug is listed for multiple connections. Usually it isn't.
wirenut1110 is offline   Reply With Quote
Old 08-08-2012, 05:43 AM   #3
Rewards Points: 510
There's obviously other methods of doing this as I've just learned on another thread. These just work for me
Old 08-08-2012, 06:00 AM   #4
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Just bond the two disconnects together and out of one of them hit your grounding electrodes.
Old 08-08-2012, 11:15 AM   #5
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
What NEC are you using?
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
Old 08-08-2012, 12:08 PM   #6
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
We run the water ground to one panel, the ground rods to the other, run a jumper between the two panels, and split bolt the jumper and each of the grounds above the panels.
Old 08-09-2012, 09:27 PM   #7
Fascinating question. Which would YOU suggest? That would be most helpful, thanks for your input!
Old 08-09-2012, 09:49 PM   #8
k_buz's Avatar
You don't seem to understand. You cannot CHOOSE which version you use, your state/community chooses for you. You need to find out which code cycle your area is under.
The Following User Says Thank You to k_buz For This Useful Post:
Evstarr (08-10-2012)
Old 08-10-2012, 10:06 AM   #9
electures's Avatar
The version adopted by your governing body.
Old 08-12-2012, 02:31 PM   #10
Rewards Points: 502
My jurisdiction required me to make one continuous loop.
I started in panel A, outside, thru the connector for grounding rod #1 thru connector on grounding rod #2 back inside, to panel B.
It had to be one piece of wire, no splices permitted.
-Andrew
DIY hobbiest
AndrewF is offline   Reply With Quote
Old 08-12-2012, 02:53 PM   #11
E2 Electrician
Haha. What he wants and what is required are not the same.
Old 08-12-2012, 02:54 PM   #12
k_buz's Avatar
I've seen a couple posts from people in that area stating the same thing. It may be some sort of local thing.
Old 08-12-2012, 02:57 PM   #13
E2 Electrician
Some sort of local confusion.
Old 08-12-2012, 03:36 PM   #14
E2 Electrician
The wire between the ground rods in either direction is just a bonding wire to augment the first ground rod, again, in either direction... not a grounding electrode conductor.
Of course, I would have made it continuous to save two acorns.
Old 08-12-2012, 10:26 PM   #15
" Euro " electrician
frenchelectrican's Avatar
KingB.,
What state or provice you are in ?? once you tell us what state or proviance we will know the code cycle due there are few differnt verison to use.
Merci,
Marc
cable line grounding amakarevic Electrical 56 05-15-2012 09:22 PM
Anyone want to take a shot at why #6 to attach antenna ground to breaker? Piedmont Electrical 44 01-08-2008 04:11 PM
200 amp panel with a 100 amp service? alexz Electrical 10 07-29-2007 10:00 PM
Grounding new service TonyD Electrical 11 08-21-2006 11:03 AM