Old 07-27-2011, 08:32 PM   #1
Ground Wire Size Question
Hello,
I'm not an electrician but I have done some wiring in my time. Where I am currently working we are installing a machine that required three phase 480 we ran three 1 AWG conductors and one 8 Awg conductor as the ground wire, the lenght is appox 150 ft. I question the ground wire size as any engineers I have worked with in the past ran a ground wire of equal size. When I questioned the person in charge about the size, he showed me in an old book he used that 8 Awg was a minimum for a ground when ruinning 1 Awg wire. I'd like to here what the truth is.
Thank You
Geezer
Suprageezer is offline   Reply With Quote
Old 07-27-2011, 08:41 PM   #2
Licensed Electrical Cont.
Speedy Petey's Avatar
The equipment ground is sized according to the overcurrent device protecting the circuit.
For a 100A circuit a #8 ground is appropriate and typical. NEC Table T250.122
I have to say, any electrician who sizes the equipment ground equal to the circuit conductors (on larger than 30A circuits) is wasting money.
Speedy Petey is online now   Reply With Quote
Old 07-27-2011, 09:13 PM   #3
I=E/R
a7ecorsair's Avatar
Speedy, but doesn't #8 need protection where #6 doesn't so #6 is easier to do??
a7ecorsair is offline   Reply With Quote
Old 07-27-2011, 09:51 PM   #4
Master Electrician
Sounds like a circuit in conduit which would be protected, yes?
brric is offline   Reply With Quote
The Following User Says Thank You to brric For This Useful Post:
Speedy Petey (07-27-2011)
Old 07-27-2011, 09:52 PM   #5
We are talking about equipment grounding conductors. Not grounding electrode conductors.
Old 07-27-2011, 10:12 PM   #6
I=E/R
a7ecorsair's Avatar
OK, I'll have to pay closer attention to detail. That 100 amp example sucked me right in to a panel
Old 07-27-2011, 10:18 PM   #7
Master Electrician
Don't you just hate when that happens?
Old 07-27-2011, 10:24 PM   #8
Electrical Contractor
kbsparky's Avatar
Speedy, you have failed to consider that the #1 conductors have been upsized from a #3, for a 100 Amp circuit.
Normally, a #8 is allowable for a 100 Amp circuit, per table 250.122. But if you consider the requirement of 250.122(B), you will have to upsize the EGC by a proportional amount.
A #1 conductor is 59% larger than a #3.
A #8 conductor is 16510 circular mils.
59% of that is 9741 circular mils.
The total of those numbers is 26251 circular mils.
A #6 conductor is 26240 circular mils, close enough for me, but a real stickler (are you paying attention, electures?) might require one to upsize again to a #4.
-KB
The Following User Says Thank You to kbsparky For This Useful Post:
electures (07-28-2011)
Old 07-27-2011, 10:41 PM   #9
Master Electrician
I don't see any mention of circuit ampacity in the OP.
The Following 2 Users Say Thank You to brric For This Useful Post:
electures (07-28-2011), Speedy Petey (07-28-2011)
Old 07-27-2011, 11:05 PM   #10
kbsparky's Avatar
Maybe not, but my response was directed to Speedy, who used 100 Amp in his example.
IF the OP is dealing with a circuit that exceeds 100 Amp, then a #6 EGC would be the minimum size required, adding more if upsizing was involved.
-KB
Old 07-28-2011, 10:45 AM   #11
Lic Electrical Inspector
electures's Avatar
Originally Posted by Suprageezer View Post
Hello,
Thank You
Geezer
In order to answer correctly the size and type of the OCPD protecting the circuit is required.
All responses based on the 2011 NEC.
If you live in New Jersey click
. All other states click
Please check with local, county and state officials as laws may vary.
Sizing motors
. Online motor calculator
. Online calculators
electures is offline   Reply With Quote
Old 07-28-2011, 01:58 PM   #12
electures's Avatar
90.1 Purpose.
(A) Practical Safeguarding.
The purpose of this Code is
the practical safeguarding of persons and property from
hazards arising from the use of electricity.
(B) Adequacy.
This Code contains provisions that are considered
necessary for safety. Compliance therewith and
proper maintenance results in an installation that is essentially
free from hazard but not necessarily efficient, convenient,
or adequate for good service or future expansion of
electrical use.
Before we travel down that road lets find out more about the machine and wiring. Don't want to get the "experts" excited yet.
Sizing motors
Old 07-28-2011, 04:00 PM   #13
You are correct, but it is feasible to use #1 on a 100A circuit and it not be upsized. #1 @ 60 deg C is only 110A.
If there are 60 deg terminations somewhere #2 or #1 would be required, yet only a #8 ground.
question on 240 wire size and ground for wall oven twobyfour2 Electrical 8 04-30-2011 08:13 AM
voltage on ground wire - multiple ground problem? Thaiman Electrical 14 04-02-2011 12:49 PM
Running new(up to code) ground wire & protection. MikeSF Electrical 25 07-04-2010 05:33 PM
Fanimation ceiling fan question: no blue wire from ceiling camrn2006 Electrical 8 03-07-2010 01:19 AM
Grounding conduit instead of using a ground wire? stringtheories Electrical 10 08-02-2008 01:42 PM