I have a question .I have plastic pipes in my house and need to install a ground rod ,so after I install the rod where do I run wire to from rod
drewsr is offline   Reply With Quote
Old 11-14-2012, 01:00 AM   #2
Rewards Points: 330
ground buss in main panel.
oleguy74 is offline   Reply With Quote
Old 11-14-2012, 06:16 AM   #3
Rewards Points: 1,506
Run the wire (#6 copper; grounding electrode conductor) non-stop from the ground rods to the main panel neutral bus.
In the main panel the ground bus does need to be bonded to the neutral bus either using a jumper bar or a #6 jumper wire or having both busses making good metal to metal contact with the panel body. A screw provided for the purpose that digs into the panel back is a suitable bonding.
You need two 8 foot ground rods at least 6 feet apart.
For those eavesdropping who already have a grounding electrode conductor non-stop from the panel to a metal water pipe exiting the house underground, the GEC from ground rods added later can be clamped onto the existing GEC if it should reach that first.
Note that the "main panel" is where the first master disconnecting switch/breaker is located, not necessarily the panel with the greatest number of branch circuit breakers.
Old 11-14-2012, 08:18 PM   #4
Rewards Points: 506
What about rural settings? Quite often the meter is mounted on a pole (not the residential structure) with a customer disconnect immediately below the meter. Then, 3 conductors (overhead or underground) feed the 1st panel of the structure. This panel possesses the ground rod, but it does not possess the "first" disconnecting means. It is at the pole. So...Is the code such that a 4-conductor service should feed the structure's first panel?
jlmran is offline   Reply With Quote
Old 11-14-2012, 08:20 PM   #5
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
That is the code with one caveat...there should be rods at the pole, the house fed with a 4 wire, and rods at the house.
Old 11-14-2012, 08:29 PM   #6
Rewards Points: 506
I've never seen grounding at the pole beyond that which comes with the pole. And I've never seen a 4-conductor main service (meaning from pole to panel). Maybe I'll look harder.
Old 11-14-2012, 08:31 PM   #7
DIY Enthusiast
sublime2's Avatar
Rewards Points: 504
Why 2 rods?
sublime2 is offline   Reply With Quote
Old 11-14-2012, 08:35 PM   #8
k_buz's Avatar
Originally Posted by sublime2 View Post
Why 2 rods?
Despite all the misinformation out there, 2 rods is code unless you can prove one rod provides less than 25 ohms of resistance to earth. Then only one rod is required.
Old 11-14-2012, 08:44 PM   #9
JOATMON
ddawg16's Avatar
Rewards Points: 1,500
Correct.....in other words....it's cheaper and quicker to pound in a second rod than do the testing........and in the grand scheme of things....most likely more reliable.
The Following User Says Thank You to ddawg16 For This Useful Post:
jbfan (11-14-2012)
Old 11-14-2012, 08:53 PM   #10
Rewards Points: 506
Reliable for what? Do 2 or 4 or 10 rods really offer significantly greater safety from lightning than 1 rod? What data set can really demonstrate this hypothesis?
Old 11-14-2012, 09:12 PM   #11
It's not for lightning protection, it's an alternate, safe path for errant current from faulty wiring, etc, to return to earth....instead of through you
mterry is offline   Reply With Quote
Old 11-14-2012, 09:14 PM   #12
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
No its NOT... it IS for lightning protection. Current does not seek the EARTH!
The Following User Says Thank You to stickboy1375 For This Useful Post:
Jim Port (11-14-2012)
Old 11-14-2012, 09:16 PM   #13
E2 Electrician
The 25 ohm rule is a hard one to swallow, no one knows why it exists, to make life easy, we drive two rods and leave it at that, hell, does ONE rod do anything?
Old 11-14-2012, 09:18 PM   #14
But it does seek the much lower resistance of a copper grounding system than, say, the impedance of human, wood, brick, glass, rubber, plastic, right?
Old 11-14-2012, 09:19 PM   #15
DIY Enthusiast
sublime2's Avatar
Rewards Points: 504
Lighting sure does though.
The Following User Says Thank You to sublime2 For This Useful Post:
jlmran (11-14-2012)
To ground or not to ground Red Squirrel Electrical 2 10-14-2010 08:42 PM
Wiring an outlet using both ground screws instead of pig-tailing together. cabber24 Electrical 5 08-26-2010 08:40 AM
Electrical Ground Problem cabinetman Electrical 15 01-28-2010 04:55 PM
Live ground wire in dryer Retired sailor Electrical 10 05-04-2009 03:26 PM
Hot Tub Install--Grounding Rod Question statgeek_rob Electrical 16 09-15-2007 02:59 AM