ground rod
I have a question .I have plastic pipes in my house and need to install a ground rod ,so after I install the rod where do I run wire to from rod
ground buss in main panel.
Run the wire (#6 copper; grounding electrode conductor) non-stop from the ground rods to the main panel neutral bus.
In the main panel the ground bus does need to be bonded to the neutral bus either using a jumper bar or a #6 jumper wire or having both busses making good metal to metal contact with the panel body. A screw provided for the purpose that digs into the panel back is a suitable bonding. You need two 8 foot ground rods at least 6 feet apart. For those eavesdropping who already have a grounding electrode conductor non-stop from the panel to a metal water pipe exiting the house underground, the GEC from ground rods added later can be clamped onto the existing GEC if it should reach that first. Note that the "main panel" is where the first master disconnecting switch/breaker is located, not necessarily the panel with the greatest number of branch circuit breakers. |
That is the code with one caveat...there should be rods at the pole, the house fed with a 4 wire, and rods at the house.
It's not for lightning protection, it's an alternate, safe path for errant current from faulty wiring, etc, to return to earth....instead of through you
But it does seek the much lower resistance of a copper grounding system than, say, the impedance of human, wood, brick, glass, rubber, plastic, right?
| All times are GMT -4. The time now is 10:39 AM. |