Ground ? In Old Two Wire Elect System - Electrical - DIY Chatroom Home Improvement Forum
Old 02-23-2009, 01:07 PM   #1
OCDiy'er
ground ? in old two wire elect system
I am installing new lighting & some outlets in a 60 year old house. It only has 2 wire electric system - hot & neutral only, no ground wire. What do you do with the ground wire that is on all the lights purchased? For the outlets can replace with polarized 2 prong outlets, but was told this not acceptable by city electrical inspector. He said if replacing must used grounded 3 prong outlet. So how does this get resolved? Can ground and neutral be joined since they both connect to neutral bus bar in panel? I did not think that was allowed.
Thanks,
Matt M
wis_remod is offline   Reply With Quote
Old 02-23-2009, 01:14 PM   #2
RippySkippy's Avatar
I generally twist it up and leave it in the box. If you wanted to you can put electrical tape around it as well.
In this situation, the only 3 prong outlets you can install are GFCI...and you would need to install one for each duplex you wanted to replace....no down stream protection...
NO! if you do and there's a short that does not trip the breaker, external surfaces will become energized...not a biggie for lights...but think about appliances....lots of opportunity for disastrous results...
when it comes to breakfast, the chicken is dedicated, the pig is committed.
LMASD
RippySkippy is offline   Reply With Quote
Old 02-23-2009, 01:37 PM   #3
OCDiy'er
Post
OK, so a GFCI can be used as a replacement in a two wire system?
Also, on the new lights I hooked up the white to white & black to black, left ground unattached. However, at the other end of the wire had both ends of wire attached together to metal frame of light. Does not seem right to me.
Thanks again,
Matt M
Old 02-23-2009, 02:42 PM   #4
yes they can.
Not sure I understand "the other end" ....are you describing the ceiling box wiring or the switch box...
LMASD
Old 02-23-2009, 03:16 PM   #5
That's not correct. As long as the circuit is GFCI protected, you can install 3 prong receps.
GFCI breakers are often the easiest solution in these cases.
As far as fixture grounds, there's not much you can do with them but cut them off or leave them hanging safely in the jbox.
220/221 is offline   Reply With Quote
Old 02-23-2009, 03:43 PM   #6
elect, contractor
Rewards Points: 27
Exclamation
Agree'd, that is actually what is required here for ungrounded plug replacements, either a gfi breaker or install a gfi plug at the panel protecting that circuit, or install a gfi in the first receptical in the circuit putting the rest of the circuit on the load side, I don't like that method as a peice of funature can be placed in front of it then it gets forgotten and when it trips ,,,,, also some of the older boxes don't have suficient space with the existing conductors to properly install a gfi. by gfi'ing all the ungrounded circuits you will also be protecting the lights as well.
the comment about jumping from the neutral to the ground on a receptical,,, definately not, thats an accident waiting to happen
ACB Electric is offline   Reply With Quote
Old 02-23-2009, 03:52 PM   #7
Licensed Pro
Thanks,
Matt M
The only way you can have a grounded 3 prong outlet is to run a new ground wire back to the panel, or rewire the circuit. A GFCI or a new 2 prong receptacle are both NEC acceptable replacements. Neither has a grounded third "prong".
Old 02-23-2009, 04:55 PM   #8
OCDiy'er
"other end" clarification
Hi again,
Thanks for your help on my questions!
The "other end" is the end of the two conductor electric wire after it runs through the three lights.
The light consists of three separate lights mount to a straight bar that is suspended from the ceiling. The wire starts with the ends that are joined with the wires in the ceiling box, then it continues through the light fixture and exits on the other side. It is this end consisting of the two wires that are joined together and fastened to the metal frame that holds the light up
that is attached to the ceiling box. To me it does not seem right - kind of like my previous point of the neutral & ground being combined not being right.
Thanks,
Matt
Old 02-23-2009, 05:02 PM   #9
You need to describe it better.
The conductors should not be tied to the fixture except at the lampholders.
The ground wire, yeah. The black and white, no.
Old 02-23-2009, 05:20 PM   #10
OCDiy'er
I didn't think that was right. Will try to get a picture.
Old 02-23-2009, 07:29 PM   #11
Rewards Points: 2,350
Everyone's answered but no one has mentioned the requirement for the supply conductors to be rated at 90 degrees C.
Old 02-23-2009, 10:02 PM   #12
That's because:
1) it's the real world
2) it aint gonna happen
3) it would just confuse him even more.
Old 02-24-2009, 07:24 AM   #13
That's because:
Hmm...I don't think I would have torn my walls up, spilled blown in insulation just to pull out that old, groundable bx out because of the darn tw insulation.
rgsgww is offline   Reply With Quote
Old 02-24-2009, 07:55 AM   #14
Rewards Points: 179
i'm SLOWLY learning electrical guys so take it easy on me here, but i thought you just connect the ground wire from the fixture/outlet to the metal box, don't you?
If its a fixture you take the ground wire from the (light) and fasten it to the metal box, and if you are going from a 2 prong outlet to a 3 prong outlet you buy some green wire and connect the green screw on the outlet to the metal box with green wire.
I thought it was that simple. and i thought that's what his question was but boy i'm seeing all these GFI replies and i'm doubting myself now.
windowguy is offline   Reply With Quote
Old 02-24-2009, 11:07 AM   #15
You can do that if you have a proper grounding path to the main panel. If you have metallic conduit (like emt) or bx (armored cable) with a bonding strip, than you can tie a ground wire to the box. If the box is metal and romex is entering, a ground still needs to be attached to the box.
Grounding conduit instead of using a ground wire? stringtheories Electrical 10 08-02-2008 12:42 PM
smoke alarm - ground wire Potomac101 Electrical 7 02-06-2008 07:25 AM
ground wire handifoot Electrical 2 06-25-2007 09:39 PM
Ground Wire Problem ScubaRaven Electrical 11 06-08-2006 02:32 PM