Ground Fault Protection - Electrical - DIY Chatroom Home Improvement Forum
Old 07-15-2011, 06:20 PM   #1
Murdy's Avatar
Rewards Points: 37
Ground Fault protection
As I understand it, one GFCI receptical will protect an entire circuit, as long as its placed first in line coming out of the box. Is this correct? My wife (who's actually pretty sharp about these things), says any recepticle within 3 feet of a water source needs to be GFCI, regardless of whether there's another GFCI breaker on the circuit. Who's right?
Murdy is offline   Reply With Quote
Old 07-15-2011, 06:24 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 648
Don't know where she is getting the 3' from, but a gfci breaker protects the entire circuit.
jbfan is online now   Reply With Quote
Old 07-15-2011, 06:40 PM   #3
Licensed electrician
Rewards Points: 1,872
A gfi receptacle can protect anything downstream if the LOAD terminals are used.
Old 07-15-2011, 08:07 PM   #4
Semi-Pro Electro-Geek
Rewards Points: 2,990
There is never a requirement that any specific receptacle *be* a GFCI receptacle, only that it be GFCI *protected*. Using an upstream GFCI receptacle or a GFCI circuit breaker is always allowed.
mpoulton is offline   Reply With Quote
Old 07-15-2011, 09:43 PM   #5
Learning by Doing
Leah Frances's Avatar
Mpoulton is right. The ONLY benefit of a 'local' GFCI rec, is that it is easy to identify when it trips and to reset it.
If I could only remember to THINK about what I was doing before I did it.
Leah Frances is offline   Reply With Quote
Old 07-15-2011, 11:37 PM   #6
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,990
There's that "water source" myth again.
There has never been a "water source" GFI requirement. I have no idea how this myth ever got started.
Old 07-16-2011, 07:47 AM   #7
Electrician
SD515's Avatar
Rewards Points: 504
While most areas that require GFCI protection are not related to distance from a water source, there 2 2008 code sections that mention distance from a sink. 210.8(A)(7) Laundry, utility, wet bar sinks, and 210.8(B)(5) Sinks [other than dwelling units]. Both sections list within 6 ft of the edge of the sink (not 3 feet).
No circuit that is already protected by a GFCI breaker will require an additional GFCI receptacle.
Kyle
Old 07-16-2011, 11:22 AM   #8
Murdy's Avatar
Rewards Points: 37
I appreciate everyone's help.
Old 07-16-2011, 08:05 PM   #9
Knucklez's Avatar
Rewards Points: 942
actually .. one thing to be a nit-pickler.. the GFI will not protect the "entire network" .. actually, it is listed how many items it will protect. how many recepticals and how many loads (lights, fans, etc.).. who knows.. maybe your house wiring is crazy and you have tonnes of stuff of of one "network" well in excess of code due to shotty work done long before you moved in.
one big difference between a GFCI receptical protecting a "network" and a GFCI breaker doing the same is cost. it is MUCH cheaper to get a GFCI receptical.
also note that there may be some issues with trying to protect sleeping dwellings with a GFCI (not sure why you would want to.. but i mention it here anyway). because these rooms must be arc fault protected. i don't know if it can ALSO be GFCI protected?
Knucklez
"if you can't be handsome, at least you can be handy" -Redgreen
Knucklez is offline   Reply With Quote
Old 07-21-2011, 09:54 PM   #10
Murdy's Avatar
Rewards Points: 37
Thanks, Knuck. We're running completely new circuits, got the wall torn down to the studs and all the old electric demoed, so won't overload.
Tripping breakers,neutrals,120 volts and 240 volts OH My!!! Stubbie Electrical 17 06-11-2011 06:09 AM
Adding a ground wire to a fixture? dkeith Electrical 2 06-01-2011 08:08 PM
240 volt load/appliance and ground vs neutral kgize Electrical 7 04-22-2010 11:40 PM
Wire Needed for GF / Arc Fault breaker jamiedolan Electrical 13 09-20-2009 08:15 AM
Removing Concrete Ridge and Ground Protection on Ground Floor RayIII Building & Construction 1 10-09-2008 02:36 PM