Ground Fault Outlet / Breaker - Electrical - DIY Chatroom Home Improvement Forum
Old 10-04-2008, 01:20 PM   #1
DIY'er
jamiedolan's Avatar
Rewards Points: 1,024
Ground Fault outlet / Breaker
If you install a ground fault breaker, you still need ground fault outlets in bathroom and kitchens right?
So what is the point of a ground fault breaker?
Jamie
jamiedolan is offline   Reply With Quote
Old 10-04-2008, 01:44 PM   #2
Rewards Points: 2,350
Jamie
No, you just need ground fault protection in kitchens and baths. How you provide the protection is up to you. A receptacle is is just cheaper and more convenient. If you install a GFCI breaker, then there is no need to install a GFCI receptacle, and vice versa. The point of ground fault breakers is that you often have equipment that must be GFCI protected that isn't a receptacle outlet. Outside post lights come to mind, or circuits for hot tubs and whirlpools.
Old 10-04-2008, 04:05 PM   #3
Electrician
SD515's Avatar
Rewards Points: 504
One or the other. The breaker will protect the entire circuit versus the receptacle will only protect itself, and anything connected 'downstream'.
Kyle
Old 10-04-2008, 04:27 PM   #4
DIY'er
jamiedolan's Avatar
Great Thanks. A few GF breakers sound much easier than messing with finding outlets that match, particularly since I am going to be changing out the breakers anyway.
Thanks again
Jamie
Old 10-04-2008, 04:33 PM   #5
Electrician
Rewards Points: 760
Just be prepared to spend big bucks, a GFI breaker is alot more expensive then a GFI plug.
darren is offline   Reply With Quote
Old 10-04-2008, 04:38 PM   #6
DIY'er
jamiedolan's Avatar
I can get the GF breakers for $30 when I buy them with my panel. The decent quality GF outlets seem to be about $12-$15. So it will be double the cost, but I will only need a few of them.
Jamie
Old 10-04-2008, 05:56 PM   #7
If you have several outside outlets on the same circuit, say one in the front of the house, one on the side, and one in the back, then a GFCI breaker might be best. Then if it trips it would be in the breaker panel. If one of the outlets was a GFCI and the other two were wired "downstream" from that outlet, then you would need to go hunting to find the GFCI outlet to reset it.
In a bathroom the outlet is right there - easy to see it and reset it.
Billy_Bob is offline   Reply With Quote
Wire Needed for GF / Arc Fault breaker jamiedolan Electrical 13 09-20-2009 09:15 AM
This doesnt seem right. JoulesWinfield Electrical 27 07-26-2009 08:40 PM
Outlet neutral bonded to ground? rjniles Electrical 1 07-19-2008 12:12 PM
Hot Tub Install--Grounding Rod Question statgeek_rob Electrical 16 09-15-2007 03:59 AM
Subpanel feeder questions Silhanek Electrical 4 03-22-2007 07:30 PM