Ground Distance From Water Entry - Electrical - DIY Chatroom Home Improvement Forum
Old 05-07-2009, 11:16 PM   #1
Ground distance from water entry
Hi guys
Does anybody know what the safe distance a ground wire can be from the water service entry? The ground is connected to a water pipe some distance from the water entry the meter is jumped
jprince is offline   Reply With Quote
Old 05-08-2009, 12:43 AM   #2
canfixmost
Not really sure what you are asking but there is nothing that says a ground wire has to be so for from a water source. you are accually required to bond your service to the water and gas system.
RenoDon is offline   Reply With Quote
Old 05-08-2009, 06:15 AM   #3
Bigplanz's Avatar
Rewards Points: 990
You can use the water system for grounding, but not gas.
Bigplanz is offline   Reply With Quote
Old 05-08-2009, 07:05 AM   #4
Someone told me that the ground should be connected as close to water service entry as possible
Old 05-08-2009, 07:58 AM   #5
Licensed Pro
If you have at least 10ft of buried metal water pipe, then that should be your primary grounding electrode. The connection to this electrode should be within 5ft of it entering the house.
Old 05-08-2009, 08:51 AM   #6
Thanks that is what I thought. I do not not know why sometimes they are placed far away to much room for error.
Old 05-08-2009, 08:54 AM   #7
Licensed Pro
If the water feed to the building is plastic, then the connection to the metal piping becomes a bonding connection. This is not part of the grounding electrode system and can be anywhere along the pipe. Jumpers across non-conductive parts are required.
Old 05-08-2009, 10:45 AM   #8
Water feed is copper
Old 05-08-2009, 03:36 PM   #9
DIY'er
jamiedolan's Avatar
Rewards Points: 1,024
250.52 Grounding Electrodes.
(A) Electrodes Permitted for Grounding.
(1) Metal Underground Water Pipe. A metal under-
ground water pipe in direct contact with the earth for 3.0 m
(10 ft) or more (including any metal well casing effectively
bonded to the pipe) and electrically continuous (or made
electrically continuous by bonding around insulating joints
or insulating pipe) to the points of connection of the
grounding electrode conductor and the bonding conductors.
Interior metal water piping located more than 1.52 m (5 ft)
from the point of entrance to the building shall not be used
as a part of the grounding electrode system or as a conduc-
tor to interconnect electrodes that are part of the grounding
electrode system.
Jamie
Jamie Dolan - Neenah, WI
Jamie Dolan Paw Dogs
Need Help Uploading Photos? Click here.
jamiedolan is offline   Reply With Quote
Old 05-08-2009, 04:06 PM   #10
Chicago, IL
Michael Thomas's Avatar
Just wanted to stress that:
as here in Chicago I frequently see DYI projects with improper or missing jumpers, here's one from last week:
__________________________________________________ ______________________
Home Inspection: "A business with illogically high liability, slim profit margins and limited economies of scale. An incredibly diverse, multi-disciplined consulting service, delivered under difficult in-field circumstances, before a hostile audience in an impossibly short time frame, requiring the production of an extraordinarily detailed technical report, almost instantly, without benefit of research facilities or resources." - Alan Carson
Home Inspections, Infrared (Thermal Imaging) Leak Identification and Inspection Services, Roof, Attic, Building, Basement and Foundation Moisture Intrusion and Water Leak Inspections, Troubled Building Consultations - Serving Chicago and Suburbs http://paragoninspects.com/
Michael Thomas is offline   Reply With Quote
Old 05-08-2009, 05:27 PM   #11
It was jumped. I am home inspector in illinois I have seen this more and more and keep on writing it up . I was just curious what the max. feet away the grounding electrode could be. I know it has to be real close These real estate agents get real mad at me to . They always say well it is grounded. They just don't understnd how important it is. I explain why but they are just worried about the deal
Very Low Hot Water Pressure. PAS1970 General DIY Discussions 2 02-25-2009 03:01 PM
low hot water pressure angus242 Plumbing 10 01-08-2009 11:41 AM
Filling a Cast Iron radiator system insulatorpro HVAC 7 10-06-2008 11:31 PM
GROUND - Wall Oven - Water Line Acceptable? Mickey53 Electrical 5 09-29-2008 12:02 PM
Periodic release from (I think) the T&P valve on the water heater alexz Plumbing 3 08-15-2006 10:31 AM