#1 |
Ground connection
Hello,
I was not able to load the national code links featured on the sticky above. As I look at my breaker box, I see three wires coming in from the street. Two go into the main area of the breakers (assume these are 120 each) and the other go to the neutral bus (where white colored wires feed). However, there is nothing going to the ground bus, and I do not see anything connecting the ground bus to the neutral bus. Should I have a dedicated wire going into the ground bus connecting it straight to the earth rod? |
#2 |
Ground connection
your post doesn't say where you are, but here in ontario, it depends on if you are city or rural. If you are in the city you need a wire from your neutral to your water pipe cityside of your water meter, if you are in the country you can use a ground plate or 2-10' ground rods, then bond your water pipe to the groundbar in your panel. In your panel there should be a black screw in your neutral bar, this is your bond screw, it connects the neutral to ground via your panel enclosure, sometimes there is a jumper that connects your neutral bar to ground.
#3 |
Licensed Electrical Cont.
Ground connection
Be reminded, a water pipe bond or electrode, or a ground rod or plate, or any other electrode, is NOT where your "ground" comes from in your panel. These items serve another purpose entirely.
The ONLY place your equipment ground comes from is the neutral/ground bond described above. This can be in several forms as described, such as a screw, strap, or the bars screwed directly to the panel box. |
#4 |
Ground connection
Thanks for your response.
This came about as my gas stove electronics have been acting up and the company claims that it needs and independent ground. The tech says I am missing a wire coming in the breaker box - should be four instead of the three in there now. One to the ground bus bar, one to ground and two hot. Last edited by frank otero; 02-14-2011 at 07:20 PM. |
#5 |
Ground connection
Does the branch circuit cable coming from the stove receptacle have a ground wire? Check to be sure it is connected properly including at the stove receptacle.
Electronic equipment can have an informal ground, a bare wire daisy chained from one piece to the next using some connection such as a screw that goes into the chassis. Connect the far end to a known ground which can be a water pipe that is all metal down into the basement and to the cold water line entering the house where in turn there needs to be a (#6 for 100 amp or smaller electrical services) copper ground wire to the breaker panel frame or ground bus. At the first panel where there is a switch or breaker that shuts off the entire power feed, there are just three wires coming in, the two hot wires for 120/240 volts and one wire that serves as both neutral and system ground. The latter has to be bonded in some fashion to both the neutral and ground busses. Such bonding is normally accomplished by having the wire connected to the neutral bus or a piece of metal hanging off of it, and the neutral bus has a screw digging into the back of the panel itself or a wire or copper strip going to the ground bus or attached to the back of the panel. The system ground is connected to ground rods at most if not all of the utility poles but must also be connected to a wire going out from the panel to the main water pipe or to a ground rod at your house.
The average homeowner who lost his house in the Oklahoma tornadoes should move for good and not rebuild. Too much complexity watchdogging the contractor. Too much a chance to be defrauded. Last edited by AllanJ; 02-15-2011 at 09:17 AM. |
#6 |
Ground connection
Thanks Allan,
My box does have the three wires (quite thick) coming in and distributed as you mentioned. There is a copper leg from the neutral bus screwed into the panel. I got continuity between ground bus bar and neutral bus bar in the panel. Took the junction box apart that feeds the stove, disconnected all wires, and got continuity between ground (bare) wire and service panel and between neutral and ground wires. My gas line (stove is gas and electric) also showed grounded. I am starting to think the stove is properly grounded. |
#7 | |
I=E/R
Ground connectionQuote:
Did he say where this missing forth wire should be connected? You do have a large bare wire connected to the ground bus, yes? That is wire # 4
#8 | |
From all I have put together, it seems that three wires is all that is required for my installation (one main panel, no sub-panel). For some reason he felt 4 wires is the code. |
#9 |
I=E/R
Ground connection
Yup, 4 wires is correct - two hots, a neutral, and the GEC (ground).
#10 |
Ground connection
Do you lack a wire running from the panel to the entering cold water pipe?
The average homeowner who lost his house in the Oklahoma tornadoes should move for good and not rebuild. Too much complexity watchdogging the contractor. Too much a chance to be defrauded. |
#11 | |
I amy put a wire between ground and neutral bars for sheeeet and giggles, but all the tests have shown that my sytem is grounded. |
#12 |
I=E/R
Ground connection
You have a correctly wired service. 2 hots, 1 neutral, and 1 ground. Believe it or not, that is 4 wires. The guy who told you that there should be 4 wires should limit his electrical troubleshooting to broken flashlights.
#13 |
Ground connection
The wire going to the ground rod is your fourth wire.
It may connect to either the neutral bus or the ground bus given that this is the panel with the main disconnecting switch and the neutral and ground busses are bonded to each other (here, via the panel metal)
The average homeowner who lost his house in the Oklahoma tornadoes should move for good and not rebuild. Too much complexity watchdogging the contractor. Too much a chance to be defrauded. Last edited by AllanJ; 02-17-2011 at 08:04 PM. |
#14 |
UAW SKILLED TRADES
Ground connection
Actually the grounding electode conductor entering the service equipment must terminate to the terminal or bus to which the service grounded conductor terminates. Terminating the GEC at the service equipment to a grounding bus is a code violation.
" One nice thing about the NEC articles ... you have lots of choices" Stubbie |
#15 | |
Can I just run a wire between ground and neutral bus bars, leaving the rest the way it is now (ground wire from outside the house is attached to the neutral side)? Can someone point to the section of the code that covers this? PS. I only have one panel...no sub panels thank you all for the responses Last edited by frank otero; 02-18-2011 at 09:02 AM. |
| Display Modes | |
| sub panel ground and neutral | daddyrabbit | Electrical | 3 | 01-29-2010 07:49 AM |
| Sub Panel Main Lug Load Center - Single Phase ? | Roy Rowlett | Electrical | 21 | 08-20-2009 07:55 PM |
| Older home -- Open Ground issues, please help | Toyz | Electrical | 1 | 06-15-2008 09:41 AM |
| Hot Tub Install--Grounding Rod Question | statgeek_rob | Electrical | 16 | 09-15-2007 03:59 AM |
| Ground rod blues!!! | ra_doliv | Electrical | 8 | 09-03-2007 12:48 AM |