#1 |
Gounding breaker box.
I am selling my home and the inspector said I need to ground my breaker box to a water line. My question is my main box is in a finished room and the nearest water line is in my garage on the opposite side of the house. I have a subpanel that runs my AC and dryer which is in my unfinished laundry room. Could I ground the subpanel to a water line in the laundry room?
#2 |
Lic Electrical Inspector
No. It has to come from the main service disconnect. Is your water main plastic or copper? Is it a home inspector?
All responses based on the 2011 NEC. If you live in New Jersey click To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. . All other states click To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. . Please check with local, county and state officials as laws may vary. Sizing motors To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. . Online motor calculator To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. . Online calculators To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. . |
#3 |
Licensed electrician
How did your inspector determine that the panel was not already grounded?
Only the service panel would be grounded to the water line and ground rods.
Answers based on the National Electrical Code. Local amendments may apply. Check with your local building officials. |
#4 |
All copper and yes it is a home inspector.
#5 |
Delete.
#6 |
No sure how he determined that it was not grounded. It is grounded outside to rod outside but no to the water line.
It is copper. |
#7 |
Can you post a picture with the panel cover off?
#9 |
how about what gauge wit do I need?
#10 |
for 100amp service using copper its #6 ...200 amp is #4. and must be connected within 5 feet of point of entrance into home.
#11 |
Does the water line coming in from the street enter in the garage? Is that where the water meter is located?
#12 |
Yes it comes In the garage and the meter is there also.
#13 |
Is there a groung rod? If so, where does the #6 CU come from? Where is the main panel in resepct to the meter?
#14 |
The inspector called you on the lack of the water pipe ground because he did not see it or find it. For a metal main water pipe exiting the house underground you need to have such a grounding as described above. It's okay for that wire (grounding electrode conductor) to go all the way across the basement from the panel with the first main disconnect switch to the water pipe.
Technically, a metal main water pipe exiting the house underground counts as a grounding electrode and all grounding electrodes must be bonded (connected together with appropriate sized wires as GECs). A metal gas pipe exiting the house underground does not count as a grounding electrode but the gas piping system should also be bonded to the aforementioned grounding electrode system. A wire similar in size to a GEC can be used; here it is called a bonding jumper. A GEC to a ground rod need not be larger than #6 copper regardless of the amperage of the electrical system.
The average homeowner who lost his house in the Oklahoma tornadoes should move for good and not rebuild. Too much complexity watchdogging the contractor. Too much a chance to be defrauded. Last edited by AllanJ; 12-01-2012 at 11:40 PM. |
| Display Modes | |
| Well pump trips breaker at start, but then starts when breaker reset | J. David | Electrical | 34 | 02-25-2012 12:23 PM |
| Outside breaker, inside main breaker panel, so is it a sub? | CPF | Electrical | 29 | 02-01-2012 11:28 AM |
| Wiring Size Calculations for New Service | CorinthWest | Electrical | 7 | 12-07-2010 12:36 PM |
| 20 Amp Breaker tripping with GFCI | panhandlion | Electrical | 7 | 12-12-2007 09:59 PM |
| Outdoor breaker panel questions | lhoney2 | Electrical | 12 | 07-19-2007 06:44 PM |