Old 09-28-2011, 05:54 PM   #16
Licensed electrician
Rewards Points: 1,018
Originally Posted by INEEDHELPPLZ1 View Post
So if I have a bunch of 15a outlets saved up, I can install them on a 20a circuit without creating a harmful situation? I always thought the outlets had to match the breaker...
The device only needs to match the breaker rating if there is only one place to plug into. A regular duplex receptacle counts as two places and are allowed to be installed on 20 amp circuits.
INEEDHELPPLZ1 (09-29-2011)
Old 09-28-2011, 08:12 PM   #17
Electrical Contractor
kbsparky's Avatar
Its possible that the OP has a surge power strip plugged into those GFCI-protected outlets.
Surge power strips will shunt the minor surges to ground, thus creating mini ground-faults. A GFCI outlet with class A protection will interpret this as a fault sufficient enough to trip out.
Try removing the surge power strip(s) and see if your nuisance tripping continues....
-KB
The Following User Says Thank You to kbsparky For This Useful Post:
Old 09-28-2011, 08:15 PM   #18
.................wrong thread
Old 09-29-2011, 06:50 AM   #19
Electrician
SD515's Avatar
Rewards Points: 504
I didn’t read each post thoroughly, but the mention of ‘cramming’ GFI’s into small metal boxes and having random trips makes me think that one or more of them may have their ground wire(s) touching the neutral terminal(s) (maybe intermittently). Under load, a short between neutral and ground will trip a GFCI (and not the breaker), as not all the current will go through the neutral, some will go through the ground wire(s).
Kyle
The Following User Says Thank You to SD515 For This Useful Post:
Old 09-29-2011, 07:40 AM   #20
Rewards Points: 79
Extra insulating
Just a thought - after reading all of the posts and figuring that some if not all are possible, I wanted to recommend wrapping electrical tape around the outlet before placing into those METAL boxes. Cheap, easy, and as you can see - would rule out some of the possible causes mentioned.
If you don't have time to do it right, when will you ever have time to do it over?
jackofmany is offline   Reply With Quote
The Following User Says Thank You to jackofmany For This Useful Post:
Old 09-29-2011, 09:41 AM   #21
I do have a 2 power strip bars plugged into the very last 2 outlets on the run....Thank you for thinking outside the box...I will test that theory
INEEDHELPPLZ1 is offline   Reply With Quote
Old 09-29-2011, 09:42 AM   #22
Good suggestion! I will implement into rework process... Thanks!
Old 09-30-2011, 09:28 AM   #23
kbsparky's Avatar
Power strips by themselves are fine. It's those that have built-in surge protection that can cause nuisance tripping of GFCI devices.
The conflict here is the GFCI units are for people protection, while the surge units are for equipment protection.
And sometimes, you can't have both
-KB
Dishwasher Tripping GFCI outlets Mikedks Electrical 16 05-30-2016 07:50 PM
2 wire outlets: connect neutral to ground? border collie Electrical 19 04-12-2013 01:29 PM
Supplemental Outlets in 1950's House Perry401 Electrical 2 05-01-2011 09:49 PM
outdoor wiring, electical outlets tripping frgwtchr Electrical 6 07-25-2009 12:56 PM
outlets work, but barely (?) joeyboy Electrical 7 08-27-2008 09:37 AM