-   -   GFI Breaker Won't Trip with tester (http://www.diychatroom.com/f18/gfi-breaker-wont-trip-tester-99420/)
nate456789 03-24-2011 10:13 AM
I recently built a pole barn.
I have 3 Square D QO 20amp GFCI breakers installed with 8 to 10 outlets on each one.
The Breaker will trip with the test button on the breaker. It will not trip if I use a tester in the outlet. The tester shows that the outlets are all wired correctly.
I even tried taking my wiggys and touch from hot to ground. and still no tripping. I was told this will always cause it to trip.
I disconnected one circuit from the breaker and tried the same test in the panel. with the gfi pigtail to the neutral bar and the neutral to the neutral bar and the wiggy from the hot to the neutral bar. That finally tripped it. Obviously the circuit is no good like that to use because it can't handle a load. But it was a sanity check.
All 3 GFI breakers will not trip.
This barn has it's own Meter. I installed 3 ground rods to make sure I have a good ground. I made sure that the green screw to in the neutral bar was in so the panel is grounded.
I have run out of options. I am afraid that it will not pass inspection if the inspector can't walk up and trip it from the outlets. I am also afraid that there is no protection if there is a problem.
I have had a couple electrician friends say not to worry about it if it trips with the test button on the breaker.
I don't want to find out the hard way that it doesn't work.
Is the circuit protected? Will it pass inspection? Does it sound like I have a problem?
Any other ideas to try? I have run out of ideas.
Thanks for any help
epson 03-24-2011 10:24 AM
This is the tester that you need for checking a GFCI
http://www.diychatroom.com/data:imag...waKKACiiigEf/Z
nate456789 03-24-2011 10:35 AM
Tester
Yeah I already have one of those. That is what I tested it with first. Then I was told to use the Wiggy's to try and trip it because it shows more of a current differential across the neutral and the hot. Which is what the GFI is looking for.
brric 03-24-2011 10:37 AM
The neutral of the circuit does not terminate on the neutral buss, it terminates on the GFCI circuit breaker.
nate456789 03-24-2011 10:39 AM
Correct. That is how I have it.
Hot to copper screw. Neutral to Silver screw. White pigtail from breaker to the Neutral buss.
epson 03-24-2011 10:41 AM
Ok if you have one of those testers did the lights turn on and show you installed it correct? If they did, did you push that button on the tester to set it off? Just asking…
nate456789 03-24-2011 10:42 AM
Yes, All orange lights showed the wiring was correct on each outlet. Pushing the tester button did nothing.
nate456789 03-24-2011 10:44 AM
Also as a sanity check I wired just one single outlet directly to the breaker. Straight out of the breaker box. Still would not trip using any of the listed methods.
epson 03-24-2011 10:45 AM
Pushing the button on the tester did nothing? That’s supposed to trip the GFCI
nate456789 03-24-2011 10:47 AM
Yes I know. That is the problem. I have pretty much tried everything I can think of.
epson 03-24-2011 10:47 AM
Could be a faulty GFCI
nate456789 03-24-2011 10:48 AM
All 3 of them? Brand new out of the box? Anything is possible I guess.
epson 03-24-2011 10:50 AM
You could also have a lose connection somewhere…
jbfan 03-24-2011 11:03 AM
Something to try is add a single receptacle, about 10 foot from the panel.
Use this receptacle as a test bed by connecting it to each gfci and then us the testers test button. button.
nate456789 03-24-2011 12:11 PM
Yep in post #8 I already tried that. Like I said I am running out of ideas. I have been trying to figure this out for a few weeks now.