Old 12-11-2008, 09:29 AM   #1
Gfi
One of my GFI's was tripped this morning and when I reset it it holds for 5-10 sec and then pops again. I unplugged everything and it is still doing it, does this mean the GFI is bad?
tedrjar is offline   Reply With Quote
Old 12-11-2008, 10:10 AM   #2
joed's Avatar
Rewards Points: 12,024
Could be bad or if it is attached to an outdoor recpetacle there could water or insects in the receptacle box. Test be removing any wires connected to the LOAD terminals. If it resets then problem is in the LOAD circuit.
Old 12-11-2008, 10:14 AM   #3
Registered User
Termite's Avatar
GFCI receptacle devices aren't high grade hardware, and do break or go bad. Sometimes replacing them with a new GFCI device will take care of the problem.
If the problem persists, your GFCI might be functioning properly and revealing a deeper problem.
The 10 second delay in tripping makes me think the device is bad.
Old 12-11-2008, 10:22 AM   #4
Rewards Points: 862
I would take Joed's advice and disconnect wires from the LOAD terminals. There could be a small amount of leakage that is causing it to trip after a short time. Of course it could also be a bad GFCI, but either way, you have to open the box and take a look.
Ultrarunner2017 is offline   Reply With Quote
Old 12-11-2008, 10:45 AM   #5
There's 6mA to 4mA leakage, according to the UL GFI (maximum) curve. With real world GFIs the current probably has to be higher than this to trip within those intervals.
With this much leakage, you might be able to measure it with an ohmmeter (less than 30 KΩ fails).
Old 12-11-2008, 08:28 PM   #6
no fuss, no muss leakage current tester
You need a digital meter on the 200vac scale. 10 MΩ input impedance for the meter is assumed for this test.
120.0vac is in series with the meter in series with the hot lead of the cable or device under test. The grounded lead of the cable or device under test returns the current to the source.
A: If the cable or device is shorted to the ground lead, you read 120.0vac.
B: If the perfectly good cable is 50' long, you read 114.3v due to normal cable capacitive reactance. Longer cables will read closer to 120.0v.
C: If the cable has enough leakage to trip a GFI within seconds, you read 119.6v.
If you shunt the digital voltmeter with a 1MΩ resistor, your readings will be
A: 120.0v
B: 80.0v
C: 116.5v
If you use a 1000Ω/volt cheapie analog meter, no shunt resistor, your reading will be (on the 150v scale)
A: 120.0v
B: 28v
C: 100v
There is no danger of blowing the meter, even if the cable is shorted.
You can see that using the cheaper meter gives you a more sensitive test.
If the cable or device passes this test, the cable or device is almost certainly not the cause of the GFI tripping.
Old 12-12-2008, 03:15 AM   #7
A: 120.0v
B: 80.0v
C: 116.5v
A: 120.0v
B: 28v
C: 100v
Let me know when you write a book. I want to buy it.
Timster is offline   Reply With Quote
Old 12-12-2008, 08:09 AM   #8
electrician
No, a good GFCI will definately trip at those levels, I have tested hundreds with the tester in the following post.
Silk is offline   Reply With Quote
Old 12-12-2008, 08:12 AM   #9
electrician
A: 120.0v
B: 80.0v
C: 116.5v
A: 120.0v
B: 28v
C: 100v
Your numbers will never be that, the voltage to your house can be anywhere from 110 to 130 volts, it jumps all over depending on the time of the day. Also the resistance of your meter leads, the resistance of your connection points, the tolerance of your shunt resistors, etc, ect, ect..........
Or, you can just get one of the following and not waste your time trying to scab together something that is already available:
Old 12-12-2008, 03:57 PM   #10
What make and model is the tester in the picture?
Old 12-12-2008, 04:00 PM   #11
Thanks.
I thought I could write until I got onto Internet forums. I come to find out that it's not that easy to write what I mean. . .
Old 12-12-2008, 06:11 PM   #12
electrician
It's a Hubbell GFT2G
Now if I wanted to test the cable I would:
1. Turn off the breaker
2. Use an ohmmeter between hot and ground
3. Use an ohmmeter between neutral and ground
4. If I have less than 120/.004=30,000 ohms between either conductor and ground, I would know the cable was tripping the GFCI.
Simple, Easy, No special setup required.
Here's a rule that I live by, it's called KISS
Keep
It
Simple
Stupid
Works for me.
Old 12-12-2008, 06:36 PM   #13
Electrical Contractor
jbfan's Avatar
Rewards Points: 254
[QUOTE=Silk;197261]It's a Hubbell GFT2G
QUOTE]
Kinda pricy for a diy'er
I have never seen one like that
How does it work
Old 12-12-2008, 07:43 PM   #14
electrician
The numbers 1 - 6 on the end correspond to 1 through 6 milliamps. As you turn the dial it diverts 1 to 6 milliamps to ground. If the GFCI doesn't trip by the time you get to 6, the gfci doesn't work.
Old 12-13-2008, 04:56 AM   #15
DIYer
I just cut the end off one of the millions of computer IEC power cables I have and then put 2 x 22kohm 1/2 watt resistors in parallel between ground and hot for a total of 11kohm 1 watt. Works great for testing GFCIs and confirming that downstream outlets are protected. Gives you about 10ma from hot to ground.
Total cost, a few cents. :P
If you want exactly 6ma, it should be about 20,000 ohms. I would use 2 x 1/2 watt in parallel (remember that cuts the ohms in half), they don't dissipate much power even in an unprotected outlet, but good to make it safer, in case some idiot leaves it plugged in..
Gigs is offline   Reply With Quote