GFCI Trip When Ground And Neutral Touch - Electrical - DIY Chatroom Home Improvement Forum
Old 10-27-2010, 01:49 PM   #1
Unhappy
GFCI trip when ground and neutral touch
I opened up a ceiling box to replace a single bulb with two fluorescent. The box was wired for two switches at opposite ends of the room. There was no ground existing, so I pulled one from another outlet to be able to ground the new lights and the box.
The 15 amp circuit is protected by a GFI breaker, as there is also a bathroom on it. If the ground wire touched the neutral, it tripped. I wired an outlet to the circuit to test it, and the lights indicated that all was well, but it bothers me that something might be amiss.
Any ideas on what might cause this? Should I be thinking about pulling new wires (please, no!)? Help!
thewoodguy is offline   Reply With Quote
Old 10-27-2010, 01:53 PM   #2
Rewards Points: 330
you are on the load side of the gfci.thats what they are supposed to do,how they work.when gnd and neutral touched there is a fault..POP.line side don't matter beacause gnd and nuetral are tied togethet in mai panel.
oleguy74 is offline   Reply With Quote
Old 10-27-2010, 02:58 PM   #3
Just call me Andrew
Rewards Points: 1,020
Why are you touching the ground wire to the neutral?
Oleguy is right, that is the GFCI operating as it should. There was a ground fault, so it tripped.
Andrew
secutanudu is offline   Reply With Quote
Old 10-27-2010, 06:34 PM   #4
That should have been obvious, but thanks for the reminder! Secutanudu, the first was by accident, subsequent were just to figure out what was going on. I feel safe now!
Old 10-27-2010, 07:17 PM   #5
Is the outlet where you are pulling the ground on the same circuit as the light ?
Old 10-27-2010, 09:06 PM   #6
@Scuba-Dave - no, it's separate. The original circuit is ungrounded. I'm still trying to assess the wiring in this place, which was done in 1957. Grounding is spotty, and often run to the nearest copper pipe! Some outlets have a thin ground wire connected to the outside, some don't. It's a mess.
Old 10-27-2010, 09:27 PM   #7
Rewards Points: 330
be extreamly careful.don't want you hurt...
Old 10-27-2010, 09:37 PM   #8
You need to run grounds back to the panel
Not from another circuit
And not to water pipes
Old 10-28-2010, 03:53 AM   #9
Seasoned DIYer
Rewards Points: 150
GFCI is a differential amplifier. Both neutral and hot are wrapped around in a coil. So, if the inbound and outbound aren't perfectly symmetrical, it sees it as a leak. When you let the neutral touch the ground, the ground wire will act as a parallel jumper back to the panel and some of the current will be diverted and shared with neutral, which causes asymmetry between neutral & hot within the GFCI. So, it will see it as a ground fault.
HVAC_NW is offline   Reply With Quote
The Following User Says Thank You to HVAC_NW For This Useful Post:
Lurlene (10-29-2010)
Old 10-28-2010, 10:09 PM   #10
I=E/R
a7ecorsair's Avatar
Originally Posted by HVAC_NW View Post
GFCI is a differential amplifier. Both neutral and ground are wrapped around in a coil. So, if the inbound and outbound aren't perfectly symmetrical, it sees it as a leak. When you let the neutral touch the ground, the ground wire will act as a parallel jumper back to the panel and some of the current will be diverted and shared with neutral, which causes asymmetry between neutral & hot within the GFCI. So, it will see it as a ground fault.
GFCI's compare the current in the Hot conductor and Neutral conductor using a coil. Touching a ground wire to the neutral will cause some of the "return" current to flow in the ground wire and some to flow in the neutral so the GFCI will see an imbalance between the Hot and neutral.
a7ecorsair is offline   Reply With Quote
The Following User Says Thank You to a7ecorsair For This Useful Post:
Old 11-01-2010, 06:21 PM   #11
Seasoned DIYer
Rewards Points: 150
That was a typo. I fixed it. Even with no load, if you short the neutral to ground, it will cause a small amount of current between ground and neutral, which the GFCI will see as asymmetry between hot & neutral, then trip.
Tags
electric wiring problems , gfci switch/outlet
240 volt load/appliance and ground vs neutral kgize Electrical 7 04-22-2010 11:40 PM
This doesnt seem right. JoulesWinfield Electrical 27 07-26-2009 07:40 PM
Ground rod or not? brotherman Electrical 30 07-15-2008 04:58 PM
Nuetral from feeder cable to main panel question? TW Lucas Electrical 14 05-08-2008 11:33 AM
Subpanel feeder questions Silhanek Electrical 4 03-22-2007 06:30 PM