Old 02-03-2011, 09:15 AM   #1
GFCI tester shows hot/ground reversed, then not reversed
I just bought a GE 50957 GFCI receptacle tester.
http://www.amazon.com/50957-Tester-I...ef=pd_sim_hi_2
I tested several receptacles last night, both GFCI and non-GFCI, all checked out ok.
This morning I checked a receptacle that is GFCI protected (downstream from a GFCI receptacle), and the tester indicated that hot and ground were reversed. I pressed the test button, and the circuit went dead as expected. I then reset the GFCI and now all receptacles on the circuit show normal.
How could the hot and ground test reversed, then not reversed?
Thanks.
bw777 is offline   Reply With Quote
Old 02-03-2011, 09:57 AM   #2
Electrical Contractor
wirenut1110's Avatar
Send a message via AIM to wirenut1110
I believe when those testers show hot/ground reversed, it's an open neutral. Sounds like you may have a loose neutral connection.
wirenut1110 is offline   Reply With Quote
Old 02-03-2011, 11:13 AM   #3
That tester has 2 functions -
one is a recptacle tester, testing the for proper wiring: hot, neutra,l and ground wires, and their respective locations. it also tests the availability of the proper voltage. the led's show status.
second is a gfci tester. when the button is depressed, it install a resistance between hot and ground so that a small amount of current passes to the ground conductor (this is a ground fault, or short) which should activate the gfci reseptacle/circuit and trip it. resetting the gfci braker is then required. i don't think it is recommended to push the button on non-gfci protected circuits, which is where you're problem may be.
TimPa is offline   Reply With Quote
Old 02-03-2011, 12:49 PM   #4
There is a different code for open neutral. But I have not checked for a loose neutral yet.
Old 02-03-2011, 12:53 PM   #5
I tested a non-GFCI receptacle, pushed the button, then tested the receptacle that showed hot/ground reversed this morning, and it tested ok.
There is a freezer on the gfci circuit, in the basement. Maybe it was running or started up when I was testing this morning and caused the reverse test?
Edit - I just read the instructions again, and it does say to unplug all appliances on the circuit before testing.
Old 02-04-2011, 09:17 AM   #6
Scared Electrician
Saturday Cowboy's Avatar
Absolutely no reason not to. It is the only way to check the operation of a protected receptical.
Ragged Trousered Philanthropist
Please follow the code - its there for your safety no matter how inconvenient.
Saturday Cowboy is offline   Reply With Quote
Old 02-04-2011, 09:47 AM   #7
are you implying the gfci test button is also recommended for testing the circuit beaker (operation) in the load panel that is protecting the wire? I guess i have never heard that, so i am curious.
Old 02-04-2011, 10:16 AM   #8
Master Electrician
The only way that tester will test a circuit breaker is if the breaker is a GFCI. Using it on a standard circuit will do nothing other than to check for correct wiring.
brric is offline   Reply With Quote
Circuit tester shows open neutral; multi-meter says something different. fredgmeyer Electrical 11 10-26-2009 01:41 PM
GFCI Tester PaliBob Project Showcase 0 10-22-2009 06:14 AM
On one outlet my GFCI tester has all three lights lit. What does it mean? Deck Electrical 6 07-09-2008 10:18 PM
GFCI Question Mdbuilder Electrical 6 06-19-2008 04:15 PM
GFCI questions 5circles Electrical 4 11-05-2007 09:24 PM