GFCI For Roof And Gutter Heaters - Electrical - DIY Chatroom Home Improvement Forum
Old 09-09-2011, 06:39 AM   #1
GFCI for roof and gutter heaters
I was told that a roof and gutter heater receptacle doesn't have to be on a gfci. It is considered to high for a person to normally reach it. WTH!
I am in articles 422 and 426 and I am lost. My head hurts.
Hourglass52 is offline   Reply With Quote
Old 09-09-2011, 07:00 AM   #2
Code05's Avatar
Rewards Points: 1,104
210.8 Ground-Fault Circuit-Interrupter Protection for
Personnel. Ground-fault circuit-interruption for personnel
shall be provided as required in 210.8(A) through (C). The
ground-fault circuit-interrupter shall be installed in a
readily accessible location.
Informational Note: See 215.9 for ground-fault circuit interrupter
protection for personnel on feeders.
(A) Dwelling Units. All 125-volt, single-phase, 15- and 20-
ampere receptacles installed in the locations specified in
210.8(A)(1) through (8) shall have ground-fault circuitinterrupter
protection for personnel.
(1) Bathrooms
(2) Garages, and also accessory buildings that have a floor
located at or below grade level not intended as habitable
rooms and limited to storage areas, work areas,
and areas of similar use
(3) Outdoors
Exception to (3): Receptacles that are not readily accessible
and are supplied by a branch circuit dedicated to
electric snow-melting, deicing, or pipeline and vessel heating
equipment shall be permitted to be installed in accordance
with 426.28 or 427.22, as applicable.
(4) Crawl spaces — at or below grade level
(5) Unfinished basements — for purposes of this section,
unfinished basements are defined as portions or areas of
the basement not intended as habitable rooms and limited
to storage areas, work areas, and the like
Exception to (5): A receptacle supplying only a permanently
installed fire alarm or burglar alarm system shall
not be required to have ground-fault circuit-interrupter
protection
Informational Note: See 760.41(B) and 760.121(B) for power
supply requirements for fire alarm systems.
Receptacles installed under the exception to
210.8(A)(5) shall not be considered as meeting the
requirements of 210.52(G).
(6) Kitchens— where the receptacles are installed to serve
the countertop surfaces
(7) Sinks — located in areas other than kitchens where
receptacles are installed within 1.8 m (6 ft) of the outside
edge of the sink
(8) Boathouses
Code05 is offline   Reply With Quote
Old 09-09-2011, 07:01 AM   #3
Licensed electrician
Rewards Points: 1,622
You were told correctly. Here is the Exception: Receptacles that are not readily accessible and supplied from a dedicated branch circuit for electric snow melting or de-icing equipment shall be permitted to be installed in accordance with the applicable provisions of Article 426.
Old 09-09-2011, 07:17 AM   #4
To late
I already have it on a GFCI breaker. Article 426.28 ? I have no idea what the tenant will do with the heater or receptacle.
I can just see a DIY tenant up there with an ax helping the heater cable because it wasn't turned on.
Old 09-09-2011, 07:18 AM   #5
Code05's Avatar
Already on a GFCI breaker.
And.....tis legal.
Old 09-09-2011, 09:36 AM   #6
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,214
Personally I would want heat tapes in a metallic gutter protected by GFCI. If you were to have a fault, the whole gutter system could be come live. Walk by and touch a downspout and OUCH! (or worse).
Coastal South Carolina
Old 09-09-2011, 01:22 PM   #7
Electrical Contractor
kbsparky's Avatar
I believe that those outlets are allowed to be protected with a GFEP breaker, which is a different animal than a GFCI breaker.
GFEP is for equipment protection and has a trip threshold of 30 mA. A GFCI breaker has a trip threshold of 5 mA, and is for personnel protection.
-KB
Gutter Heaters DrKatieRN General DIY Discussions 8 03-26-2012 12:11 PM