Gfci Receptacles Wire Continuity Test - Electrical - DIY Chatroom Home Improvement Forum
Old 03-04-2010, 11:50 AM   #1
Thumbs up
Gfci receptacles wire continuity test
Hello,
2 neighbor GFCI recptacles in mi kitchen are controlled by different breakers. Both of them are of the tripping kind but one of them does not tripp. I don't know whether it is because the tripping mechanism is stuck or simply, it was set up for not to trip since the very beginning.
In a continuity test between them I found out that there is continutiy for the ground wire. That means that these 2 receptacles are linked by the ground wire.
The question is: there should be ground continuity for them if they do not belong to the same circuit?
Thank you for your answer
Hialeahn is offline   Reply With Quote
Old 03-04-2010, 12:04 PM   #2
Licensed electrician
Rewards Points: 1,616
It would be simpler if you just turned off the one breaker for the GFI and see if the other one goes off also.
All of the circuit grounds should be connected in the panel.
Hialeahn (03-04-2010)
Old 03-04-2010, 12:31 PM   #3
Correction: the 2 receptacles belong to different circuits
Originally Posted by Jim Port View Post
Iit would be simpler if you just turned off the one breaker for the GFI and see if the other one goes off also.
Thank you for your reply.
Old 03-05-2010, 07:38 AM   #4
Of more concern is the fact that your GFCI outlet is not tripping. This usually indicates a miswire...ie...load and line wires reversed. This is a very important safety feature anywhere near water....that these pop when an appliance or electricity would be discharged into you rather than it's intended path. Line is the side of a GFCI where the electricity or hot wires are coming in....Load is the side where the normal travel wire is then energized by electricity b/c the GFCI allows it through. Have an electrician look into it for your safety.
Affordable7 is offline   Reply With Quote
Old 03-05-2010, 06:52 PM   #5
Electrical Contractor
kbsparky's Avatar
Or it could be a bad unit. Older units when they go bad simply just won't trip, but they still provide unprotected power at the receptacle.
-KB
GFCI between porch receptacles Thurman Electrical 4 08-19-2009 12:40 PM
Outlet is dead but ears are hot!? Whassup? Hubandwif Electrical 33 03-23-2009 08:01 PM
GFCI receptacle/switch for disposer resourcefultami Electrical 8 02-23-2009 12:21 AM
Leviton 8599 GFCI wiring issues Ultrarunner2017 Electrical 4 02-06-2009 08:53 AM