GFCI Receptacle On GFCI Circuit Breaker - Electrical - DIY Chatroom Home Improvement Forum
Old 12-01-2010, 11:17 PM   #1
GFCI receptacle on GFCI circuit breaker
This seems obvious, but I thought I'd ask. Our lav has a GFCI receptacle that includes a switch for the shower fan, but the entire circuit is on a 15a GFCI breaker. Is this redundant, and would it be kosher to just use a combo switch/receptacle and mark it "GFCI Protected" instead? I'd like to use the combo GFCI on another circuit, and avoid paying for one I might not need.
Thanks!
thewoodguy is offline   Reply With Quote
Old 12-01-2010, 11:23 PM   #2
Electrical Supplier
Rewards Points: 150
I dont see why not.
LyonsElecSupply is offline   Reply With Quote
Old 12-02-2010, 10:05 AM   #3
I understand, even, that GFI devices on top of GFI devices to be counter-productive (they cease to operate properly when you install a GFCI device on a circuit that is already so protected.) One per circuit is sufficient.
oberkc is offline   Reply With Quote
Old 12-02-2010, 02:37 PM   #4
joed's Avatar
Rewards Points: 11,606
FALSE. They operate just fine. You just never know which one will trip for the fault or maybe they all will if wired to each others LOAD side.
Tags
gfci switch/outlet
New Fluorescent Ballast trips GFCI Breaker?? marc515 Electrical 7 02-18-2010 05:42 PM
New circuit breaker owen22 Electrical 14 01-12-2010 08:08 PM
Heat pump circuit breaker pbms pinkertonpv HVAC 11 02-18-2009 10:47 AM
Old Electric Panel/ Circuit Breaker Box dankreboot Electrical 3 12-16-2008 01:52 PM
Kitchen outlet breaker simma Electrical 3 02-28-2007 06:50 PM