GFCI Receptacle - Electrical - DIY Chatroom Home Improvement Forum
Old 01-24-2007, 08:00 AM   #1
Rewards Points: 123
GFCI receptacle
What is a GHCI receptacle and what is it use for? How does it work? Should all receptacles in the bathroom and laundry room be GFCI? How do I tell the difference between a line and load wire? Can they be connected to the same post on a receptacle?
jerry1967 is offline   Reply With Quote
Old 01-24-2007, 09:39 AM   #2
JoulesWinfield's Avatar
I believe GFCI stands for Ground Fault Circuit Interrupter.
On the back of a GFCI receptacle it should be clearly marked "Line" and "Load".
NEC2002, 210.8 - "All 125-volt, single-phase, 15- and 20-ampare receptacles installed in the locations specified in (1) through (8) shall have a ground-fault circuit-interrupter protection for personnel.
(1) Bathrooms
(2)Garages, and also accessory buildings that have a floor located at or below grade level not intended as habitable rooms and limited to storage areas, work areas, and areas of similar use.
Exception No.1: Receptacles that are not readily accessible.
Exception No.2: A single receptacle or a duplex receptacle for two appliances located within dedicated space for each appliance that, in normal use, is not eaisly moved from one place to another and that is cord-and-plug connected in accordance with 400.7(a)(6), (a)(7), or(a)(8).
(7) Laundry, utility and wet bar sinks - where the receptacles are installed within 1.8m (6 ft) of the outside edge of the sink"
As Ive stated here before Im not totally fimilar with residential code, but I think this should cover your question.
JoulesWinfield is offline   Reply With Quote
Questions About Changing GFCI receptacle to a normal three pronged outlet LYTTONJ Electrical 11 05-04-2011 02:23 PM
New GFCI Breaker Tripping w/ 3-way Flourescents BigJimmy Electrical 8 12-29-2008 02:29 PM
Kitchen outlet breaker simma Electrical 3 02-28-2007 05:50 PM
Split Receptacle on 3-Way Circuit NPS Electrical 6 11-03-2005 09:28 AM