Old 03-10-2011, 10:10 AM   #1
GFCI at recep or in panel as breaker
A new kitchen will have a single above-counter-in-backsplash duplex receptacle located where a countertop microwave oven (estimated at 1100W) will be located. The single-outlet circuit will be 20A.
Immediately to the R, the countertop ends at the refrigerator recess. A single duplex receptacle in the wall behind the fridge for powering it. Once again, one outlet circuit, 20A.
We know the single circuit for the MW must be GCFI protected per NEC 2008. May the GFCI protection be by means of a GCFI receptacle, with the breaker being a non-GFCI Square D HOM120 breaker? Receps are a lot less expensive than breakers.
How about the one for the fridge? It is down near the floor. Must that circuit be GFCI?
JohnstownFlood is offline   Reply With Quote
Old 03-10-2011, 11:01 AM   #2
no on the fridge.no gfci nedded.
oleguy74 is offline   Reply With Quote
Old 03-10-2011, 11:03 AM   #3
Licensed electrician
Under the NEC only the receptacles that serve the countertop require GFI protection. This can be provided by a GFI breaker or GFI receptacle. The receptacle is much cheaper and easier to reset if it ever trips.
A receptacle behind the frig does not require GFI protection.
15 AMP GFCI and breaker panel 8roty Electrical 6 01-04-2010 08:10 PM
Proper cable entry into breaker panel tns1 Electrical 12 08-27-2009 12:25 AM
New GFCI Breaker Tripping w/ 3-way Flourescents BigJimmy Electrical 8 12-29-2008 03:29 PM
20 Amp Breaker tripping with GFCI panhandlion Electrical 7 12-12-2007 09:59 PM
breaker panel Ehren51 Electrical 1 01-28-2004 08:43 PM
